O
Octopus
Well .... the mi says 16a
So a dedicated circuit required ...
So a dedicated circuit required ...
I agree, as I said before I had no intention of doing it any other way, I just wanted to satisfy my own curiosity about the potential consequences of connecting to a standard 3 pin plug / socket. Thanks for your helpWell .... the mi says 16a
So a dedicated circuit required ...
I agree, as I said before I had no intention of doing it any other way, I just wanted to satisfy my own curiosity about the potential consequences of connecting to a standard 3 pin plug / socket. Thanks for your help
I completely agree with you, as I said in my original post I had no intention of connecting to a 3 pin plug. I fully appreciate that the regs and max current ratings are there purely for safety and under no circumstances should they be exceeded.It is not something you can say “it’s only a little over”
The limit is 13A, not 13.2A not 13.05A
13A IS THE MAXIMUM.
End of discussion.
I didn’t think it would be as simple as that somehow so I either need to buy an oven under 2.9kW that has a plug fitted or get a sparky to run a new cable from the CU with a 16Amp MCB?Yes, you are way off the mark. It is not permitted to connect loads greater than 13A to a ring final.
All connections to ring final circuits must have a fuse of no more than 13A (usually a fused BS1361 plug or an FCU).
In fact, the guidance is that fixed loads of more that 2KW should be on their own dedicated circuit.
Hi - the common approach for providing power to electric cooking appliances is by their own circuit. While the design can vary, its often a 6mm cable with a 32A overload protective device. The actual appliance connection method used is then varied to suit the appliance.I didn’t think it would be as simple as that somehow so I either need to buy an oven under 2.9kW that has a plug fitted or get a sparky to run a new cable from the CU with a 16Amp MCB?
Shame you weren't on our negotiating team for Brexit !It is not something you can say “it’s only a little over”
The limit is 13A, not 13.2A not 13.05A
13A IS THE MAXIMUM.
End of discussion.
NOCould be way off the mark here.... if the existing socket was off a RFC then the MCB would be rated at 32A.
Would it be possible / acceptable for an electrician to remove the existing socket and fit a cooker control unit, providing the cable to the oven is suitably sized, say 6mm?
I do have a cooker circuit but as far as know that’s for the electric hob on the other side of the room.Hi - the common approach for providing power to electric cooking appliances is by their own circuit. While the design can vary, its often a 6mm cable with a 32A overload protective device. The actual appliance connection method used is then varied to suit the appliance.
Are you saying you have no cooker circuit?