Re: Hot Tub Tripping

why have you started another thread with an identical post ?
bad form to be honest.
 
Re: Hot Tub Tripping

Right been over to see the hot tub myself and what he told me is ******** he got of the internet and what he thought was tripping!

This is the situation with the Hot Tub:

Make: Balboa Water Group
Ran from garage consumer unit from main board in kitchen via a 50amp mcb to the garage consumer unit which also has 50amp mcb (so no discrimination) then to an isolating switch for the hot tub then to hot tub.

It is fully earthed and is protected by a 30 mA rcd, performed ramp test and ittrips at 23.0 mA.

It is ran in 10mm Armoured cable so plenty big enough.

Hot tub runs fine and starts up you can select the 2 modes of bubbles and it works fine all the lights are on it works fine, when the thermostat clicks the heating on, it shows the light and stays on for about 30 seconds then trips the Rcd.

Read more: http://www.electriciansforums.net/e...ons/62192-wiring-hot-tub-2.html#ixzz24TiygYrk
Yep, 30 second delay till the thermo controller ( West? Eurotherm? Omron? Something like that) finished initializing itself, then the heater contactor kicks in
then the faulty heater trips the RCD.

Hard water, scale on e heater, can't dissipate the heat to the water, expands, cracks, ...
 
Two separate threads on the same question is going to cause confusion for those who are trying to assist you. I've merged both threads into one for you.
 

Reply to Wiring Hot Tub in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
191
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Electrician Jobs TT supply for hot tub
Thanks for the advice so far. I now have a local qualified electrician engaged with this and an installation plan for TT earth at the hot tub and...
Replies
15
Views
1K
To the OP, the majority of French rural properties are TT with the connection exposed to the elements, with the below disconnection device bolted...
Replies
8
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top