When it goes against the manufacturers instructions???

Is this a theoretical question, or have you come across it on a job?

Isolators, it probably doesn’t matter as it’s just a switch… but mcbs and RCDs it will
 
if you get it the wrong way round the fuses remain live when the isolator is switched off.
One reason I like the Schneider "Quadbreak" style of fused-switch is they isolate both sides of the fuse, so you can feed either way and don't have to worry if the load is UPS-y and leaks a lot even with the supply disconnected (i.e. potentially both sides are "live").

MCBs probably not an issue.

Some RCDs can have trouble if powered from the load-side as stuff like test button is not disconnected when they fire and so can burn out. However, many RCD are OK from either end but it can be hard to get a definitive statement on that.
 
As above, according to manufacturers instructions. Where I am domestic and commercial CU's / distribution boards are almost always wired with supply on top and final circuits on the botton of circuit breakers / RCD's.
 
When I spoke to hager tech about this they said that mcbs must be fitted the correct away round as I remember it ,it was to do with the direction the arc traveled in the event of a fault or overload
 
When I spoke to hager tech about this they said that mcbs must be fitted the correct away round as I remember it ,it was to do with the direction the arc traveled in the event of a fault or overload
I’ve been told the exact opposite from Hager technical support, direction doesn’t matter and doesn’t effect operation at all.
 
When I spoke to hager tech about this they said that mcbs must be fitted the correct away round as I remember it ,it was to do with the direction the arc traveled in the event of a fault or overload
When fitted to a DB/CU yes, but that is to do with the mechanical arrangement and possible results of arc gasses on the cables, etc. Not electrics as such. Also some MCB do not have identical clamps on either side, so there is a further mechanical reason for which end is on the busbar.

Some MCB rated for DC use do have a direction/polarity, but for AC I can't see any reason.

As far as up/down is concerned typically on a type A board the main switch or incomer RCD is fed from the top, but then the MCB/RCBO is fed from the bottom. However, for type B boards of course it is left/right!

I asked Hager once for the RCCB in a DIN board and was told either way is fine, as I checked the data sheet, etc, and at no point did it suggest a direction, but I wanted to be sure.
 
The MI tell you which end to connect to the busbar, and which end goes to the outgoing circuit.

Do they? The MI for a DB will tell you which way round they should be installed in that DB, but the MI for the actual circuit breaker is unlikely to say anything about it.

If you fit a circuit breaker incomer to the DB then you will have the live side at the bottom of the incoming circuit breaker and the live side at the top of the outgoing circuit breakers.
 
This is what I got on 22/6/2020

Good Morning [pc1966],
Apologies for the delay, in regards to your question, the answer is no.
Our Main switches & RCD are neither pole dependant and makes no difference if you feed the supply from the top nor bottom.
I hope this answers your question.
Kindest regards,
Fraser
Technical Support

Hager Ltd
Hortonwood 50
TELFORD,Shropshire TF1 7FT
United Kingdom
 

Reply to Wiring supply in top of Isolators RCDS and mcbs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
366
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
334
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
371

Similar threads

View: https://www.youtube.com/watch?v=glsg2HpWyok
2
Replies
21
Views
897
  • Question
The legs on the bus bar are too long for the new rcbos
Replies
3
Views
390

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top