I'm not disputing any of this..I know it is totally impractical to cut a notch to 50mm deep. I was just trying to point out a confusion on page 59..fig 7.1 clearly states that a notch is a route for a cable to pass through it..above fig 59 it states that any cable passing through a joist should be 50mm from the top. So if we were to take this literally a notch should be 50mm deep, if they were to make this clearer there should be 2 diagrams. 1 showing cables passing through a joist i.e a hole and 1 showing dimensions of a notch. Anyone in agreement???
 
It tells you the maximum depth your notch can be in relation to your joist. If this is less than 50mm then it must satisfy the other stated requirements to comply. Simples.
 
IMHO where you put the notches and holes is building regs,
Where you run cables is wiring regs.
Yesterday's cables are "selected and erected" to yesterday's wiring regs.
When you select and erect it has to be to BS7671:2011. In this case 522.6.100.
That means just because there's a convenient hole in the joist doesn't mean that you can use it for twin&earth, unless of course you fulfil one of the conditions for mechanical protection. I don't have sufficient wisdom to assert whether a notch plate is sufficient protection.
Interestingly the 50mm is from the top or bottom of the joist not the surface of the floor or ceiling, i.e. does not include the depth of the floorboard. Strange.

Laurie
 
Interestingly the 50mm is from the top or bottom of the joist not the surface of the floor or ceiling, i.e. does not include the depth of the floorboard. Strange.


​that's to allow for 3" nails. bear in mind that the average wood butcher or wet-head will use whatever he has to hand when nailing boards.
 
How daft, old houses often have joists with more holes than Swiss cheese and they seem to stay up.

that's because they were built, not thrown up designs by pencil pushing bean counters.
 
I could not care less about BS7671, the first priority of any trade working on site is make sure that at the end of it he/she has not weakened the structure, stuff the regs, use what's there and inform the IET to issue a guideline of old houses with existing holes in joists (weakened joists). Holes in joists should never be allowed in the firstplace!! or should be thinker than required in the first place to conpensate for electricans and plumbers
KC
 

Reply to wiring through joists. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
400
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

See there is the problem. I can put back to way it was. Is it safe, in my opinion NO!! It's wasn't safe before the incident. No Fused Spur...
Replies
9
Views
535
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top