Another quick question I'm sure one of you will have the answer to...
I am going to be running cables under my floorboards but as the house is over 100 years old this has been done many times before. The joists have already been notched out but not to the latest depth as per regs i.e 'in a zone between 0.07 and 0.25 x span'. Would you need to re-notch in the correct zone (weakening the joist further) or can you use the existing.
Also the regs state that a cable passing through a joist should 'be at least 50mm from top or bottom' on the same page it states that the max depth of a notch is '0.125 x joist depth'. That would mean a joist would have to be 400mm to achieve this and seeing as I don't live in a castle my joists aren't that depth.
Cheers in advance
Another quick question I'm sure one of you will have the answer to...
I am going to be running cables under my floorboards but as the house is over 100 years old this has been done many times before. The joists have already been notched out but not to the latest depth as per regs i.e 'in a zone between 0.07 and 0.25 x span'. Would you need to re-notch in the correct zone (weakening the joist further) or can you use the existing.
Also the regs state that a cable passing through a joist should 'be at least 50mm from top or bottom' on the same page it states that the max depth of a notch is '0.125 x joist depth'. That would mean a joist would have to be 400mm to achieve this and seeing as I don't live in a castle my joists aren't that depth.