Wiring up garage lighting
The rcbo in the house was just to isolate the circuit from the rest of the house. If the cable gets cut or damaged in the garden, I don't want anything else being affected in the house. I could have fitted another rcd + MCB instead but there wasn't room on the board. The RCD in the garage is for the garage circuits. I didn't see the need to add another main switch in the garage. Is that against regulations?
The point is that you have put two RCDs in series which does not comply. It raises the question of why you have provided RCD protection to the SWA distribution circuit which is normally unnecessary?
Purely to keep any moisture out. They are installed inside the garage but my sockets, switch and cu are all waterproof. OTT maybe but I'd rather play it safe
You say you’d rather play it safe but you won’t even pay for an electrician to check the work you have done? This is nonsense, if you wanted to play it safe you would employ a competent electrician.
Instead you have carried out the work yourself and created an installation which, based on what you have said, is non-compliant and dangerous.
Non compliant; fine. I can change it. I can't see that's in any way dangerous though
If you cannot see what is obviously dangerous then how can you consider yourself competent?
An OCPD rated higher than the connections on a single point radial is dangerous.
A lighting circuit with no functional switching and relying on the mcb for functional switching is incredibly poor design.
Good, what will you change it to?
What is the EFLI of the distribution circuit?
Looks like I'll need to use another MCB on the distribution board then.
If you think I need a 16a type C for the 16a socket that's easily changed too. Can you explain why its ok to run 13a sockets through a 32a circuit then?
I obviously wouldn't have the first clue about how to calculate the efli of the distribution board and I don't need to. As I said Ill get a qualified electrician to check everything before powering on. Thank you though. You've given me some useful advice
No, but if you want a third party to test and sign it off it needs to be compliant.
If you have a 16A socket fed from radial circuit you want the protective device to be no higher than 16A.
I didn't ask for advice. I asked if my wiring would work and if there was an easier way. You have advised me to pay for an electrician to do my donkey work though. Thanks for taking the time to reply but Ive explained that I've already done the work. You could save yourself the trouble next time.
Well that's that then.
Thanks for the advice Pete but if I need a 20mm hole drilling through the wall of MY house, a hole jigsawed through the ceiling of MY bathroom and a trench dug through MY garden, I'll be doing that myself thanks.
OK well that's me told then
I can't see this happening, as you didn't do it for the original install, as the electrician would have commented on the 20A breaker on a 16A socket. This is entirely up to you at the end of the day...
I think everyone is wasting their breath here. The OP has made it clear they will do what they want, and the forum has made it clear that they shouldn't be.
Neither side is likely to change their tack, one through ignorance and stubbornness, the other through an educated and experienced view and stubbornness.
Let's call it a draw.
Joe,
Toneyz,