Thought i'd share this one that happened to me today....

Was wiring up a customer gazebo with BG weatherproof fittings (light switch, sockets, JB and mains board). Anyway, all went fine and was on to testing the circuits.... circuits all tested fine.

The lighting cables were terminated into a JB for the time being as the customer does not have the lights yet. So, once I had finished and just by chance i thought i would use my voltage pen on the connectors just to prove the light switch was off. Pen lit up but the switch was off? Scratched the head..... used my voltage tester and was getting 108 volts with the switch off!

The BG outfdoor light switch has a neon on it via a resitor on the lead between common and one way terminal..... guessed that this was the problem rather than a faulty switch so removed it which in turn completely removed all voltage when the switch was off.

Very dangerous if you were relying on the switch to isolate the power so thought i would share.

Anyone else come across this before??
 
Shins to ----. There's ya zones. ;)

Spider method. Seen a few spots wired like that. Never a full floor!

It was the most common method in years gone by I'd say, long before looping from light to light was conceived. Also a very simple method when rewiring as you only need one cable from each switch and light and just a single 3 core and cpc to each 2 way switch. Of course for upstairs rewiring in an accessible loftspace I'd revert to the usual loop in method.
 
It was the most common method in years gone by I'd say, long before looping from light to light was conceived. Also a very simple method when rewiring as you only need one cable from each switch and light and just a single 3 core and cpc to each 2 way switch. Of course for upstairs rewiring in an accessible loftspace I'd revert to the usual loop in method.
I always thought loop in was the original method with the octopus method being the bodge type jobby.
Every days a school day huh
 
Last time we used it it fed the 5amp table lamp sockets and the switch wire. Was perfect for this instance. Done neatly and methodically it works and easy to understand if accessed.
 
Last time we used it it fed the 5amp table lamp sockets and the switch wire. Was perfect for this instance. Done neatly and methodically it works and easy to understand if accessed.
Of course everyone has their methods,
Find it more bizzare that it's older than loop in! :D
Must be a whole lot of cables to one connection unit?
I'm fasinated on how it's done now
 
Of course everyone has their methods,
Find it more bizzare that it's older than loop in! :D
Must be a whole lot of cables to one connection unit?
I'm fasinated on how it's done now
Can save a lot of cable feeding each 5amp socket instead of looping it around a room, especially if dropping from above. The switch wire is operating all the sockets for table lamps. Usually only posh people have this, the rest of us reach over the sofa and flick the rocker!
 
To be fair the ones I have seen were terminated absolutely beautifully. The sparky obviously took pride in his work and was nice to see.

On the other hand I was at a fairly new build last week (around 10 year old) and you should have seen the state of the consumer unit. It's like it was done as a temporary fix just to get the power up and running. Just shook my head
 
To be fair the ones I have seen were terminated absolutely beautifully. The sparky obviously took pride in his work and was nice to see.

On the other hand I was at a fairly new build last week (around 10 year old) and you should have seen the state of the consumer unit. It's like it was done as a temporary fix just to get the power up and running. Just shook my head
It's nice to see when someone's taken pride in what they've installed. Was at a job with Paul M couple years ago and was given the task of fixing the alarm. Took the cover off to see the back of it signed.

And ah the classic "looks alright from my house" install :p
 
Can save a lot of cable feeding each 5amp socket instead of looping it around a room, especially if dropping from above. The switch wire is operating all the sockets for table lamps. Usually only posh people have this, the rest of us reach over the sofa and flick the rocker!
Yeah makes sense. Saving half the cable on the run.
Only installed a couple recently actually in leeds. Never knew they were a thing!
Thought 5amp sockets went away yonks ago.
Used to have them years ago in the bedroom(usually the only socket) for heaters to stop the windows frosting, right?
 
Unfused plugs specially for lighting to keep the loading down - you'd have to know exactly where all your furniture was going to stay as you wouldn't want to have trailing leads if you repositioned later date.
 
Davesparks, why don't you just troll off somewhere else. Sick of your superior smug replies to everybody. It got like this before and all that happens is people start leaving the forum.

I'm not trolling, only speaking my mind just as I do in the real world.
My replies aren't superior, we are all equal here and entitled to our opinion.

If you don't wish to read my posts then use the ignore function.
 

Reply to woah! Danger present with BG outdoor light switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top