Thought i'd share this one that happened to me today....
Was wiring up a customer gazebo with BG weatherproof fittings (light switch, sockets, JB and mains board). Anyway, all went fine and was on to testing the circuits.... circuits all tested fine.
The lighting cables were terminated into a JB for the time being as the customer does not have the lights yet. So, once I had finished and just by chance i thought i would use my voltage pen on the connectors just to prove the light switch was off. Pen lit up but the switch was off? Scratched the head..... used my voltage tester and was getting 108 volts with the switch off!
The BG outfdoor light switch has a neon on it via a resitor on the lead between common and one way terminal..... guessed that this was the problem rather than a faulty switch so removed it which in turn completely removed all voltage when the switch was off.
Very dangerous if you were relying on the switch to isolate the power so thought i would share.
Anyone else come across this before??
Was wiring up a customer gazebo with BG weatherproof fittings (light switch, sockets, JB and mains board). Anyway, all went fine and was on to testing the circuits.... circuits all tested fine.
The lighting cables were terminated into a JB for the time being as the customer does not have the lights yet. So, once I had finished and just by chance i thought i would use my voltage pen on the connectors just to prove the light switch was off. Pen lit up but the switch was off? Scratched the head..... used my voltage tester and was getting 108 volts with the switch off!
The BG outfdoor light switch has a neon on it via a resitor on the lead between common and one way terminal..... guessed that this was the problem rather than a faulty switch so removed it which in turn completely removed all voltage when the switch was off.
Very dangerous if you were relying on the switch to isolate the power so thought i would share.
Anyone else come across this before??