Went to a callout today, every time the pump on a solid fuel system kicks in the dvd player turns off for a second then comes back on,the same applies when the pump turns off. The system was on a plug top plugged into the ring. I checked all connections and were fine. I then ran an extension lead off the cooker and plugged the system in, it worked fine with no disturbances to the dvd player, so assuming i had a fault on the ring i ranround with a martindale, no wiring faults. I then ir'd said ring main, all >13 mega ohms and decent end to ends too. I then made sure all circuits were seperate e.g immersion mcb only switched immersion,, cooker only switched cooker and so on. I then changed dp on immersion circuit to a single socket and plugged it in to prove my earlier findings with extension lead. I turned high stat to pull in pump and the dvd player went off again. Custoomer has changed her dvd player and it doesnt happen when standard tv is being watched. I am stumped to say the least, i had 2 thoughts in mind, the first was maybe the pump is leaking current to earth and the dvd player doesnt like it, the second was to admit momentary defeat and post it on here! Any help gratefully received. Ben
 
Can you give some info on the pump that seems to be causing the issue? What size motor is it? What type of motor is it ie shaded pole, PSC, CSR, CSIR, CSCR etc? Is the motor starting under higher load than it ought to be? Is it starting cleanly ie is there any chattering of the contactor, start relay or centrifugal start switch or any signs of the motor being short-cycled?
 
Have you checked all terminations are sound at DB?

has he checked all terminations are sound everywhere more like..

caus all we`v heard so far is a bit about goin round with a plug-in tester...and an IR test...
P
sod all said about end to ends ...

which is where he should have started really....isn`t it...


Jesus glenn that was a bit harsh, measure twice cut once should be altered to read twice then type once for you haha!
 
.[/QUOTE] The OP does say decent end to ends but no figures. I like the approach of the OP too, thoughtful, explains what hes done unlike other posts tonight![/QUOTE]

Thanks Murdoch, if i was on the pc i would like your post but im on the tablet sorry mate!
 
has he checked all terminations are sound everywhere more like..

caus all we`v heard so far is a bit about goin round with a plug-in tester...and an IR test...

sod all said about end to ends ...

which is where he should have started really....isn`t it...

"I then ir'd said ring main, all >13 mega ohms and decent end to ends too" That may have had something to do with it FFS.
 
Can you give some info on the pump that seems to be causing the issue? What size motor is it? What type of motor is it ie shaded pole, PSC, CSR, CSIR, CSCR etc? Is the motor starting under higher load than it ought to be? Is it starting cleanly ie is there any chattering of the contactor, start relay or centrifugal start switch or any signs of the motor being short-cycled?

Ive made the (potentially foolish) assumption that we are talking about a circulating pump in a heating system, but await correction by the OP
 
(Trainee, so bear in mind that some of what follows may be utter cr@p)

You mention solid fuel - out in the sticks by any chance? Reason I ask, (my understanding is that) if you're a long way from the substation/transformer with a relatively low current capacity supply cable - larger resistance - then any extra loads will lead to a larger volt drop than usual. If the motor is pulling a large current at start-up, then this could cause a temporary voltage drop that affects your DVD player.

(EDIT: We had this where we lived when I were a lad. Long way from substation. Poor overhead lines. My poor Commodore 64 was forever glitching and resetting, and it took so long to load Horace Goes Skiing as well!)

That might be part of the problem, but you said that if plugged into the cooker socket it was ok.

Same principle also applies on the final circuit. 20m of 2.5mm on L and N is about 0.3 Ohms, if your pump is briefly pulling 30A that's 9V. If the DVD player is sensitive then this could cause it to throw a wobbly.

How to diagnose? I (naive trainee) would consider doing the following:

- measure r1 and rn on your RFC
- measue the voltage drop with a fast-reaction voltmeter when you switch the pump on/off (on the same cct)
- measure the current pulled by the pump as it's turned on: either use a plug-top power/voltage/current meter, make up a plug to socket extension lead in singles and stick a clamp meter around L or N
- see if the above 3 measurements follow Ohm's law
- see if you can get any specs on the pump (particularly start-up current) - it may be faulty, or there may be a problem with the installation

Whatever it is, hope you find it, please let us know how you fixed it :)
 
Last edited:
All normal domestic size circulator pumps are either PSC or electronically commutated PM. I'd hazard a guess this one is a regular PSC motor and the switching transient (not starting current, the radio-frequency interference spike caused by the closing and opening of stat contacts) is being picked up by the DVD player via the circuit. If that is the case, you won't find any electrical fault, or excess voltage drop, or anything like that. The test would be to fit a transient suppression VDR across the pump.

I've had this in various guises - Plasma screen goes off when the electric blinds hit their lower limit, lighting presets erase themselves when the motorised screen retracts. It was always a switching transient and the VDR or other suitable suppression always cured it.

FWIW, DVD players often have global power supplies that will work all the way down to 90V, in which case voltage drop is unlikely to be the cause. Some home electronics are unreasonably touchy about interference, it would be interesting to know if the replacement DVD player was the same model as the original, in which case it could be a design fault with that model. They are not usually earthed nor are the power supplies very heavily filtered.

I am not sure about the phone charger. The current there is so incredibly tiny that I can't see any electrical factor being the cause unless there really is a loose connection nearby and dropping the phone on the base disturbs it. But RF, the phone or charger could be emitting a burst of interference at the moment the two connect.

E2A more thoughts about testing, if you don't have a scope or a meter with graphing function to log the voltage, plug a low wattage filament lamp into the same socket as the DVD and have a de-tuned AM radio nearby. When the pump starts, if the lamp flickers but there's no 'pop' from the radio, it's voltage drop, vice versa it's interference. I would think that a voltage sag bad enough to crash a DVD player would be visible on a 40w lamp but again it could be a faulty design that's hyper-sensitive. Any significant switching spike usually makes itself heard on a portable AM radio.
 
Last edited:
sorry for the lack of replies, I fell asleep! it is just a run of the mill central heating pump! thanks for all the replies , I've got a lot more to go on now! I'd reached the stage where I was considering telling her she had ghosts haha!!
 

Reply to work this one out in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top