Wago along with a Wago enclosure, in the floor space.There is no enough slack, unfortunately. What kind of maintenance-free joints do electricians use in the UK?
Well whatever cert does apply in NI then Westward 10 if any.I don't believe Minor Works Certificates are applicable in the Republic of Ireland.
So you inferred in you previous. can you suggest an alternative method or are you just being obtrusive?I don't believe Minor Works Certificates are applicable in the Republic of Ireland.
The first thing I would note is that there is red and black insulation on the conductors. Either this installation is quite old indeed (red & black went out in about the '80s off the top of my head) or was wired in incorrect colours.Regulations differ in the UK to the Republic of Ireland so alternative measures may be required. @Risteard will advise better if he sees this.
One thing that has me confused is with the age of the installation (taking account of the wiring colours) why the socket-outlet is at that height. New work must be within the range of 400mm to 1200mm - perhaps it is lower there and I've just misjudged from the picture. If the socket-outlet is rewired it will have to be set at this height.
The first thing I would note is that there is red and black insulation on the conductors. Either this installation is quite old indeed (red & black went out in about the '80s off the top of my head) or was wired in incorrect colours.
As for minor works these do not have to be certified, but if a Registered Electrical Contractor (REC) carries out the work then the customer has a right to request that a Cert No. 3 is issued with the "minor works" box ticked. Cert No. 3 is the certificate for works which do not require DSO involvement. (Prior to the introduction of Cert No. 3 there was a "Declaration of Compliance with ET101 for Minor Electrical Installation Works".)
But as the OP has stated that he will involve a REC to repair this then the REC should be able to advise on the best course of action. Certainly with the obvious damage I would be expecting that length of cable to be replaced - ideally back to the outlet it comes from.
One thing that has me confused is with the age of the installation (taking account of the wiring colours) why the socket-outlet is at that height. New work must be within the range of 400mm to 1200mm - perhaps it is lower there and I've just misjudged from the picture. If the socket-outlet is rewired it will have to be set at this height.
Indeed, sorry for the confusion. I wasn't suggesting that it was new work but that the electrical installation might be substantially old. As such there may be many other issues which should be dealt with (e.g. undersized tails; inadequate Earthing, bonding and neutralising; unearthed switches etc.; possibly no RCD on socket circuits and perhaps old Diazed fuses).I don't think the socket is new work. The existing wiring got damaged during other works.
It's not an issue for the old wiring, but the 400mm is to the bottom (not the top).The house was built in the 80s, so it might be an old original cable there. I've measured the 400mm is to the top of the socket-outlet. Is that OK?
Indeed, sorry for the confusion. I wasn't suggesting that it was new work but that the electrical installation might be substantially old. As such there may be many other issues which should be dealt with (e.g. undersized tails; inadequate Earthing, bonding and neutralising; unearthed switches etc.; possibly no RCD on socket circuits and perhaps old Diazed fuses).
It's not an issue for the old wiring, but the 400mm is to the bottom (not the top).
My point is that if it is rewired then it will have to be raised to the new height.
My god, that looks like a downlight sticking out of it! ?You are right... the replacement of the fuse board is planned. This is how it looks now, old fuse, but I have RCD at least. I'm not sure how to handle the other possible issues you have mentioned.
View attachment 56159
Got it. Thanks!
My god, that looks like a downlight sticking out of it! ?