Discuss Workers accidentally cut the wire... I'm looking for advice. in the UK Electrical Forum area at ElectriciansForums.net
The REC should advise when replacing the distribution board, as we are required by RECI and the CRU to ensure that the tails are adequate (16mm^2 is the minimum permitted by the ESB - if you have old 6mm^2 tails for example then they will have to be replaced), that the main equipotential bonding conductors are sized correctly (minimum 10mm^2) with a minimum 10mm^2 Earthing conductor to the Earth electrode. Your main protective conductor (neutralising link) will, if not 10mm^2 be replaced with a 16mm^2 conductor - this would typically have been 10mm^2 before the T&E was replaced in 2017.I'm not sure how to handle the other possible issues you have mentioned.
I have a feeling that is an emergency light
It's a Diazed fuse.Industrial type fuse I think. Can't remember the proper name.
The REC should advise when replacing the distribution board, as we are required by RECI and the CRU to ensure that the tails are adequate (16mm^2 is the minimum permitted by the ESB - if you have old 6mm^2 tails for example then they will have to be replaced), that the main equipotential bonding conductors are sized correctly (minimum 10mm^2) with a minimum 10mm^2 Earthing conductor to the Earth electrode. Your main protective conductor (neutralising link) will, if not 10mm^2 be replaced with a 16mm^2 conductor - this would typically have been 10mm^2 before the T&E was replaced in 2017.
But your REC should advise on all of this.
If you don't have an isolator or meter with an inbuilt isolator and contractor's seal (realistically it's unlikely that you will for the age of the installation) then you will need to log a job with the ESB and pay them for the tails to be upgraded. The REC will provide a Cert No. 1 to this end.
Tel, Are these the same quality as Wagos?1 of these beautys, also with heat shrink over to reinstate the sheathing.
In Line Spring Lever Connectors 3 Pole 32A
dog's danglies mate. rated @ 32A. quality appears robust.Tel, Are these the same quality as Wagos?
They look very handy.