Working in domestic properties - how responsible are you? | on ElectriciansForums

Discuss Working in domestic properties - how responsible are you? in the Domestic Electrician Forum area at ElectriciansForums.net

Joined
Mar 2, 2020
Messages
5
Reaction score
0
Location
Swindon
Hello

Over the last 2 weeks I have been doing some electrical work for the neighbour of my Daughter as they had been let down by 2 other Electricians. I normally do design work but am 18th Edition C&G 236 qualified, as I am waiting to start a new draughting contract I have been doing installation work mainly for family. My daughter told her neighbour that I was an Electrician and might be able to help them out! This neighbour told her that it was just a couple of extra sockets. Later I learned I was expected to create new 13A socket and FCU positions, move the cooker cct and add additional lighting points.
As we had the first meeting and discussed the job, the kitchen fitter/carpenter wanted a new ring main and a new cooker cct. The house owner however wanted the ring main and cooker ccts extended. I decided to go with the house owner and extend the ring main and cooker ccts. This I thought was better as I am not Part P registered and this work would not be notifiable
During the work I carried out insulation resistance tests on the original cooker cct and the new legs of the ring main. As I was told that new plasterboard was soon to be fixed to the walls.
These tests all returned values above 999M ohms. All good, I then decided to do an earth fault loop impedance test on 2 of the existing sockets, one read 1.7 ohms and the other 1.9 ohms. I believe the max value for a 32A EN60898 type B mcb cct is 1.1 ohms.
I know I will have to resolve this problem as when I have to connect the new cables into the existing ring main cables the new sockets will be over the 1.1 ohms also.
So I'm thinking I will need to check the terminal connections of all the existing socket outlets on this existing ring main and retest for Zs.
Yes I should have carried out an EICR but was told at the outset it was only a couple extra sockets needed!

Thanks in advance

Humdrum.
 
You should resolve the Zs situation before any plastering happens, if that 1.9 ohms is genuinely the Zs of the circuit before you extend it you could be up a creek after everything is plastered and you have to start running a new circuit in!
It could cost you more in making good than you were going to make on the job, unless you can get your public liability insurance to pay for it.
 
Hello

Over the last 2 weeks I have been doing some electrical work for the neighbour of my Daughter as they had been let down by 2 other Electricians. I normally do design work but am 18th Edition C&G 236 qualified, as I am waiting to start a new draughting contract I have been doing installation work mainly for family. My daughter told her neighbour that I was an Electrician and might be able to help them out! This neighbour told her that it was just a couple of extra sockets. Later I learned I was expected to create new 13A socket and FCU positions, move the cooker cct and add additional lighting points.
As we had the first meeting and discussed the job, the kitchen fitter/carpenter wanted a new ring main and a new cooker cct. The house owner however wanted the ring main and cooker ccts extended. I decided to go with the house owner and extend the ring main and cooker ccts. This I thought was better as I am not Part P registered and this work would not be notifiable
During the work I carried out insulation resistance tests on the original cooker cct and the new legs of the ring main. As I was told that new plasterboard was soon to be fixed to the walls.
These tests all returned values above 999M ohms. All good, I then decided to do an earth fault loop impedance test on 2 of the existing sockets, one read 1.7 ohms and the other 1.9 ohms. I believe the max value for a 32A EN60898 type B mcb cct is 1.1 ohms.
I know I will have to resolve this problem as when I have to connect the new cables into the existing ring main cables the new sockets will be over the 1.1 ohms also.
So I'm thinking I will need to check the terminal connections of all the existing socket outlets on this existing ring main and retest for Zs.
Yes I should have carried out an EICR but was told at the outset it was only a couple extra sockets needed!

Thanks in advance

Humdrum.
Do you have a specific question. Humdrum
 
Doh should have taken some readings first! Too late now! I would be tempted to do some further testing first, what were your end to end ring values and R1+R2, has it RCD protection for the circuit? Could it be the RCD causing the high Zs readings? And what is the main Ze for the property?
Sy
 
Check the Ze before carrying out any works to see if it is high to begin with
Not always. Repairs due to a damaged radial circuit wall cable (picture fitting), not wired in correct zone. Dug out and repaired and then a terrible Zs reading.
I found it was a Ze problem but a previous check wouldn't have made any difference, whatsoever.
Any installation work, I agree.
 
Today new kids on the block would say Rcd it.
But we’re old school.
Its also the problem of the customer,your addition wI’ll be ok, it’s the connection to it the problem.
Re test the Zs,,check continuity etc.
 
Today new kids on the block would say Rcd it.
But we’re old school.
Its also the problem of the customer,your addition wI’ll be ok, it’s the connection to it the problem.
Re test the Zs,,check continuity etc.
He's installing sockets, it will have to be RCD'd. Old school or not with 30ma RCD protection to the circuit then the maximum Zs permitted for the 60898 MCB need not apply and the maximum Zs for an RCD can be used. Nevertheless the reading is higher than expected and should be investigated...assuming of course it is a TN system which has not been stated by the OP.
 
First thing to do with a plug in tester lead is to plug it in press test then un plug it and try this several several times to see if the result changes...
Is it just high on just two of the sockets or all the socket...
 

Reply to Working in domestic properties - how responsible are you? in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Most manufacturers recommend them to be fitted. We are required to take that into account. If they had been fitted clearly it would have been...
2
Replies
27
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top