Does anyone here have any information on working as an electrician in South Africa? Do they follow the same regulations as in the UK?
Appreciate any assisitance
Matt
 
Sorry meant "bonded" not earthed. Terminology. Parts to be bonded. Min bonding conductor size 2.5mm
.6.13.2.4 Roofs, gutters, down pipes and waste pipes​
If a building is connected to an electricity supply, the roof(s), gutter(s),down pipe(s) and waste pipe(s) shall be bonded and earthed and theresistance of the earth continuity path shall not exceed 0,2​
Ω, unless
Amdt 4​
a) the supply voltage does not exceed 50 V,b) the supply uses an underground service connection,c) the roof is made of, or covered with, non-conductive material,d) the gutter(s), down pipe(s) and waste pipe(s) are of non-conductivematerial, ore) the gutter(s) and down pipe(s) are attached to a metal roof that is​
covered with non-conductive material.

No mention disconnection times in the SANS0142 book. Just must disconnect in time. Its all based on the UK regs book anyways just a LOT more basic. No adibatic equations in thsi electricians bible. The Regs exam over here, however, is INSANELY hard, Pass rate 2% - 3%(!!!!) I was told. The testing course you have to do was so simple my mum could have passed it(slight exageration but compared to Uk test and inspect its quite funny)

 
Are these all metal structures as well? I can understand if you have a metal framed building as just like here in the UK you bond it to the main MET, but if the building fabric is brick or wood with a metal roof I don't think I would be bonding it.

Is it to do with transient voltages from lightening?

Lightning protection and surge protection are not covered by the main South AfricanSANS 0142domestic regs. Surge protection is covered in SANS 61643

Compulsory earth bonding of television antenna is a fairly recent ammendment.

SANS0142
6.12.3.2 The following conductive parts do not need to be earthed:
...........
g) structural steelwork, including items such as fire escapes and cat
ladders; and
...........


6.13.2 Parts to be bonded
6.13.2.1 General
The parts given in 6.13.2.2 to 6.13.2.5 shall be bonded.
6.13.2.2 Hot and cold water systems
Hot and cold water systems shall be bonded together and also be bonded
to the earth continuity conductor system.
6.13.2.3 Antennas
An antenna (including a satellite dish) shall be bonded to the installation
earthing system by means of a conductor of at least 2,5 mm2 copper or
equivalent. Amdt 1; amdt 4
6.13.2.4 Roofs, gutters, down pipes and waste pipes
If a building is connected to an electricity supply, the roof(s), gutter(s),
down pipe(s) and waste pipe(s) shall be bonded and earthed and the
resistance of the earth continuity path shall not exceed 0,2 Ω, unless
Amdt 4
a) the supply voltage does not exceed 50 V,
b) the supply uses an underground service connection,
c) the roof is made of, or covered with, non-conductive material,
d) the gutter(s), down pipe(s) and waste pipe(s) are of non-conductive
material, or
e) the gutter(s) and down pipe(s) are attached to a metal roof that is
covered with non-conductive material.
6.13.2.5 Water pumps

Every domestic installation is also required to have an earth bar (usually in the roof space) for other services to use.
6.11.5 A readily accessible earthing terminal shall be provided for the
bonding of other services such as a telephone, an audio system, a video, and
the like, to a building. Such an earthing terminal shall be bonded to the
consumer’s earth terminal by a conductor of at least 6 mm2 copper or
equivalent, and shall be identified by the earth symbol
 

Reply to Working in South Africa in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
224
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Hello, Is anybody aware of any UK groups or organisations that volunteer or subsidise trades people to do work for; Low income/Vulnerable/Needy...
Replies
0
Views
174
yeah I know it it is tough Brad, but keep going mate, chin up and all that, if you keep going something will go your way.
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top