Yes, the regs say 5% max which is 11.5V
Yes and no.
If it was designed for 16A of typical load then it would meet the VD requirement, and without any special design information you would assume that a 16A MCB means it is designed for a 16A load.
However, if you need more than 16A because it covers a lot of rooms with various significant loads then you will simply trip the MCB. So in that case you have failed to design for the
required use.
For something like a set of sockets what constitutes the correct design load is not hard and fast. If you look in the OSG it has typical coverage area for 20A radial, 32A radial, and 32A RFC circuits and for a lot of cases that is your reasonable usage.
However, if you have a non-domestic system it can go far in the other directions:
- For example you might have 6 * 32A sockets in a factory but only one mobile item that uses them so you can design for 32A.
- Or you might find you have 6 * 13A sockets in a commercial kitchen and they all get loaded to pretty close max at the same time so a 32A RFC is not enough and you need two 32A radials or similar.
It depends, and in many cases not a lot. The ESQCR states that the nominal supply voltage should be 230V -6% +10% which is 216V to 253V and if your combination of supply voltage and circuit VD keeps the appliance voltage within that range then all equipment should work normally.
If the voltage drops very low then some equipment will malfunction and in unusual cases even be damaged by out of range operation.
In reality if you have found an unacceptably large RFC as this appears to be you need to make a judgement call about what to do. The first aspect is if it is safe or not, and that comes down the protection being able to act quickly. In today's "RCD everything" situation that should be simple but many folks like myself like to see a sporting chance that it could disconnect on the OCPD side safely, which comes down to the worst-case Zs and the MCB choice. That depends on your R1+R2 as well as Ze, so it is more than just the VD value (but they are closely related as VD depends on R1 of course).
The second aspect of the judgement is if the circuit is likely to cause trouble, and if it has been used for years without complaint then you have a reasonable answer "no". For example, you might have a very long RFC feeding a handful of sockets in an attic conversion, in which case are you likely to need 26A for any normal activity?
So while it is not compliant, if it is unlikely to lead to problems then I would leave it with a note to that effect. The only way to serve more current is to rewire some or all in 4mm or similar, dropping the MCB to 20A or 16A might make it design-consistent but it does
not help the person who needs any more current.