The installation is TT.
The meter box has been moved by the DNO. The tails will now be >3m so I will be fitting a switch fuse. I was planning on removing the DP switch in the switch fuse and replacing with a 100mA S type RCD. I would have put one in place of the main switch in the CU so this seems like a better idea as it will give greater protection to the tails as well.
My question is, do the tails and main earth still need to enter the main consumer unit through a gland or could they just go in through one of the knock outs? I always use a gland to keep them secure as if the tails ever came loose inside the CU the main fuse would not trip, however in this case the RCD would trip, so is the gland necessary?
The meter box has been moved by the DNO. The tails will now be >3m so I will be fitting a switch fuse. I was planning on removing the DP switch in the switch fuse and replacing with a 100mA S type RCD. I would have put one in place of the main switch in the CU so this seems like a better idea as it will give greater protection to the tails as well.
My question is, do the tails and main earth still need to enter the main consumer unit through a gland or could they just go in through one of the knock outs? I always use a gland to keep them secure as if the tails ever came loose inside the CU the main fuse would not trip, however in this case the RCD would trip, so is the gland necessary?