As @davesparks says, you have to confirm it really is two separate rings. Before the discussions on the wisdom (or otherwise) of that configuration is resumed it is worth noting that question has been discussed in a lot of detail recently:

More importantly if you do put them on separate MCB is to make sure they are separate - a 'figure of eight' on two parallel MCB is very dangerous as you have 2.5mm cable on what is essentially a 64A circuit!
 
Last edited:
took one set of legs out of the breaker and the downstairs sockets didn’t work
There is also this thing called a test meter...

Really, check the rings are complete, loop resistances are OK (L-L matching N-N, E-E in ratio), and properly labelled. Finally once all fitted, and both MCB open, double check the lives are still isolated.
 
There is also this thing called a test meter...

Really, check the rings are complete, loop resistances are OK (L-L matching N-N, E-E in ratio), and properly labelled. Finally once all fitted, and both MCB open, double check the lives are still isolated.
checked continuity on ring L to L N to N cpc to cpc had a full ring on both legs so put them into separate b 32 mcb mm consumer unit was dual split rcd job was complete how ever i had crossed neutural which tripped was a nightmare jobs completed and sorted now
 

Reply to wylex mcb in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

However it's done, you need to have a guarantee of no sharp/unprotected edges that can damage the insulation. Personally, I'm not that impressed...
Replies
2
Views
426
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top