K7665sMET this is the product code if you google it will show you the consumer unit not sure what type of mcb would go in this wylex board
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss wylex mcb in the UK Electrical Forum area at ElectriciansForums.net
yeah sorry totally ment mk what mcb type for this thank youK7665 is an MK part number, so a wylex mcb will not be suitable.
thank-you mate someone has put the upstairs ring and downstairs ring on one 32A mcb surley i need to change thisApparently that CU is one of the Sentry range so I guess any of the matching MCBs would do:
thank-you mate someone has put the upstairs ring and downstairs ring on one 32A mcb surley i need to change this
took one set of legs out of the breaker and the downstairs sockets didn’t workThat all depends on why you are there and what you are doing?
Firstly how have you confirmed that two rings are connected to one MCB?
There is also this thing called a test meter...took one set of legs out of the breaker and the downstairs sockets didn’t work
checked continuity on ring L to L N to N cpc to cpc had a full ring on both legs so put them into separate b 32 mcb mm consumer unit was dual split rcd job was complete how ever i had crossed neutural which tripped was a nightmare jobs completed and sorted nowThere is also this thing called a test meter...
Really, check the rings are complete, loop resistances are OK (L-L matching N-N, E-E in ratio), and properly labelled. Finally once all fitted, and both MCB open, double check the lives are still isolated.