hi folks, thought I’d share this...

Called out to a customer of mine yesterday, said that her shower switch had been making a smell if shower had been on for 10mins. Went there expecting to be a loose neutral like I’ve seen before.

The shower was a 9.5kw that had been installed and once I looked into the circuit it was a 45 amp rewireable fuse with only a 6mm cable! Connections were tight after all but the neutral side was very very burned on the load side.

As a temporary fix, I changed out the wire for 30 amp wire in the short term. Explained this to the customer as I put an amp meter on and ran the shower as she’d had it set. It ran to 42 amps - and the fuse wire held up! Set her shower to medium setting and ran the meter again and was only pulling 23 Amps.

So, if there was ever a reason to explain to customers why to upgrade their boards from fuse wire - this is a good story right here. Very dangerous and could have been a fire.
 
Jeez, I see the righteous police are straight onto this one eh? . “Temporary fix” means “temporary” until the job gets done properly!

The cable was re-terminated and switch replaced. The customer wants a quote for replacing the shower cable to a 10mm one and changing out the consumer unit.

This was 5pm on a Saturday afternoon. There was no need to just disconnect her shower completely when there was a work around as a “temporary” fix when I get back to replace
 
So you’d rock up to a customers house -disconnect their shower and walk away until you tell them you’re returning to replace their shower cable? If it was a modern day board - you’d not just de rate the MCB in the meantime to match the cable size as a temporary fix? Exactly
 
So you have admitted the cable is under rated for the maximum load, yet have left it in service? If you think that fuse wire will protect the cable then I suggest you look at the relevant curves for it and see how long it would take for it to operate at the maximum load?
 
The circuit has been de-rated and the customer has been told to leave her shower at medium setting until the changes can be made. I don’t know where you guys come from but up here you can’t get a drum of 10mm cable or a new consumer unit at 5pm on a Friday.
 
The circuit has been de-rated and the customer has been told to leave her shower at medium setting until the changes can be made. I don’t know where you guys come from but up here you can’t get a drum of 10mm cable or a new consumer unit at 5pm on a Friday.
screwfix open till 7.00pm.
 
The circuit has been de-rated and the customer has been told to leave her shower at medium setting until the changes can be made. I don’t know where you guys come from but up here you can’t get a drum of 10mm cable or a new consumer unit at 5pm on a Friday.

Doesn’t matter you have admitted leaving the circuit in a situation which could lead to a fire. Why you fitting a new DB? Could you not just fit a RCD next to the existing board?
 

Reply to Yesterday’s callout - a close call in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It looked like the live connection side ( internally) burned against the neutral of the main switch
2
Replies
23
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top