I am away to start testing a shop which has a ze of 8.34 and has no rcd protection on any circuits, should this be code 1 on condition report and should I shut off power and install a tt system until an earth can be provided by supplier. ??
 
Do you know that it's not already a TT because it doesn't sound like you're too sure what's going on there earth wise.
 
What are the earthing arrangements?
 
Tns 3 phases,clamp round old supply cable which has the metal sheath under the cloth type material, tried testing directly on to the supply cable sheath aswell as on clamp both around 8.4
 
On a lighter note, I had a Ze of 0.01 yesterday and that's testing it properly!!!
 
Ok given what it is, it's the responsibility of the DNO to maintain the earth they provide so get on the phone to them but be prepared to spend a very long time explaining the problem to a bunch of numpties who have no clue what you're talking about
 
ĂŚ you in london theyll probably charge you heavily for to fix it or tell you to supply your own earth rod. And 0.01 ! That's low. Either pme, joint box where e and n are connected or that house is right next door to a secondary sub.
 
Which area of Scotland?
And you didn't use a Megger 1700 series on 2 lead LOW did you by any chance? (I know it's obvious but thought it best to ask).
 

Reply to Ze 8.34 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top