Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.

Ze do you contact the electrical board?

And zs what would be the options?

Thanks once again

Chris
 
Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.

Ze do you contact the electrical board? only if it's a TN system

And zs what would be the options? rewire circuit in larger cable, fit a lower rated MCB,

Thanks once again

Chris

my comments in red
 
Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.

Ze do you contact the electrical board?

And zs what would be the options?

Thanks once again

Chris
If it's a TN (S/C-S) then contact the DNO to rectify (or the may say it's ok, depending on what reading it is).
If it's a TT system then you'll need to try and get the reading down.

Assuming the above are ok, then for Zs, assuming your r1 and r2 are ok (and R1+R2 is ok), either break down into separate circuits or use larger cable etc
 
So for instance if i got a ZE of 0.07 and a PFC of 3.5 KA on a 30 A BS3036, what would I need to do then? Especially if budget is at almost zero? Install rcd isolator on the tails?
 
So for instance if i got a ZE of 0.07 and a PFC of 3.5 KA on a 30 A BS3036, what would I need to do then? Especially if budget is at almost zero? Install rcd isolator on the tails?
Depends on what the suppliers fuse is in that case. The BS3036's are normally rated to 2KA max, so you are then reliant on the suppliers fuse, so probably ok. What's rcd protection got to do with this? Are you suggsting installing that to overcome the breaking limit on the BS3036's?
 
I got that impression from Marniks post someone could do that. I'm getting a bit confused. So the only way to overcome the problem would be to change the DB then? RCD is only for residual current not over current.

oops :6:
 
Hang on a mo. Quick reset. What problem are you suggesting needs to be overcome, maybe I've got the wrong end of the stick here (wouldn't be the first time :))?
 
That the PFC at 3.5 KA is too high for the BS3036 30A Fuses.

Problem is that I have fed a 2X 32A RCBO's from the 2X BS3036 30A fuse so that the Ring main and new load cable for the cooker circuit I have added to is compliant. Some of the cables are in plastic oval at a depth less than 50mm so therefore require RCD protection.

So I put in a 4 way fuse board with just the 2 RCBO's in.

Also there fore the installation still has one point of isolation.
 

Reply to Ze and zs testing! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
673
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
300

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top