I had a ze on pme of 0.55 rang up dno they said they'll not be doing anything... Rang up Niceic they said leave it if dno has said to....as long as zs is ok.... Right ok that totally under minds the bgb.
 
I had this problem a few years ago. My Ze reading was 10 ohms. After retesting a few times to double check and check again I rang the dno(Scottish power) and they were out within the hour, dug the pavement up and repaired the supply cable. All done within 4 hours.
 
I had a ze on pme of 0.55 rang up dno they said they'll not be doing anything... Rang up Niceic they said leave it if dno has said to....as long as zs is ok.... Right ok that totally under minds the bgb.

I would imagine there are plenty of TNC-S conversions out there with around the Ze 0.55 ohm. Basically means that like many other older converted TN-S cables, they are in the process of full PME conversion!! So long as your Zs values are conforming well, and have additional RCD protection, then you should be fine!!! The BGB and DNO Code of Practice's are very different animals!! ...lol!!
 

Reply to Ze of 3.39 ohms!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
614
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
2K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top