I did find this nugget in the Unite Electricians Guide to Inspection and Testing on page 74, Ze on existing installations; "On periodic inspections it is not necessary to disconnect the main earthing conductor whilst this test is performed". Presumably because you're mainly looking to confirm the presence of a reasonably low earth connection at the origin of the installation, be it TN or TT.
I do not agree with this. Perhaps Unite could have worded it more like "it's not always practicable to disconnect the main earthing conductor".
Wherever it IS practicable to do so, it should be disconnected for the Ze test. I have come across several installations that have somehow lost the connection to the suppliers earth, and the Ze reading was perfectly fine with the earthing conductor connected (due to parallel bonding connections). In fact I had one only yesterday. An upstairs flat that takes it's supply from a common service head in the downstairs flat. An electrician had done some work in the downstairs flat and had disconnected the earthing conductor for the upstairs flat for some reason. I had to reconnect it.
Of course I realise domestic is usually much simpler, and switching off the supply to conduct a proper Ze test is usually straightforward. But my point is, that the Unite statement is implying that it is ok on every periodic inspection to leave it connected. Hmm...
 

Reply to ZE on a factory in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
7K
suffolkspark
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top