W
wayne
i prefer measurement over calculation ,just to be sure nothing's amiss
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ze on earth rod in the Talk Electrician area at ElectriciansForums.net
yeah and i suppose on a minor works your measuring r1+r2 and Zs anyway so yeah at least you know its all ok, regardless of the earthing arrangements.
the above Zs mentioned was comin in at 1.63 ohms, regardless of the 90 odd Ze reading...
question is been on a job today and earth at electrode was 40 ohms and Zs's through out the installation were all averaging between 26.8 - 27.4 ohms, in the regs there are recommended max Zs's etc and also this 1667 ohms thang as well applyig if circuits are protected by 30ma rcd (which they all are in this case)
is it acceptable on a TT DIC to record these high Zs readings in there relevant box? (measured max Zs etc)
and also why on this job am i getting high Zs's yet on the job earlier mentioned in this post they are something like normal?? is this down to parrellel paths again??!!
sorry im going on about stuff!!
rich
bump!