Ze - zs = r1 + r2? | Page 3 | on ElectriciansForums
  • Thread starter conorchapple
  • Start date
  • Replies 37
  • Views 20K

Discuss Ze - zs = r1 + r2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Do you disconnect all the parallel paths when measuring then??

Bad practice my arse.
of course it's bad practice. R1+R2 should be measured before the circuit is energised. otherwise, how do you ensure that it's safe to power up?
 
Just to stick my two penneth worth in... In my opinion it is bad practice to calculate R1+R2. This is a basic dead test that proves the installation is safe and correct.
However, I think It is perfectly acceptable (and maybe even safer) to calculate Zs (Zs= R1+R2 + Ze) as You will always get the worse case scenario and It saves removing any live accessory covers etc.
So IMO if you can be sure no one has 'tampered' with any of the install between Dead and live tests then I cant see a reason why You cant calculate Zs.
 
of course it's bad practice. R1+R2 should be measured before the circuit is energised. otherwise, how do you ensure that it's safe to power up?

My bad, I quickly read this and thought it was a debate on calculating vs measuring Zs, not reverse engineering Zs by subtraction.

Apologise.
 
Hello
I may be simple missing something here but if you put a link in at the board to measure your R1R2 and test at the last point. Surely you could still get a parallel path measurement. As the earth is connected to the met at the board. Or is that simple incorrect. As a z's is testing the earth loop and not just a low ohs resistance test?
 
Hello
I may be simple missing something here but if you put a link in at the board to measure your R1R2 and test at the last point. Surely you could still get a parallel path measurement. As the earth is connected to the met at the board. Or is that simple incorrect. As a z's is testing the earth loop and not just a low ohs resistance test?
Indeed you could. We can both pretend that this is a very current thread.
 
Well it was just the most relevant one. So what if you can explain is the difference then between measuring the parallel path with a Z's as opposed to the R1+R2?
Are we suggesting that one should really remove the cpc and test the circuit individually. Otherwise I am still in the dark as to why the parallel path causes an issue for one test but not the other.
 

Reply to Ze - zs = r1 + r2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
265

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top