Inteificio

Hi.

Am working in a factory, most of the machinery on the main floor is fed from are fed from spurs (2/3 machines per spur).

As they have all been fitted with D type breakers, we need a tight Zs.
We have not got it.

I am trying to think of the easiest way of fixing it.
Turns out I'm not 100% sure what you can do with CPCs.

If each circuit has it's own dedicated CPC, can I also link a supplementary CPC (or even make a link between each CPC to have a star supplementary earth in addition to the original?)
I've flicked through the regs and can't find any info on supplementary earths!

The way I read it, is as long as all the CPCs are in the same enclosure you can do what you want!

Anyone with a bit more experience got a few tips?

Thanks,
 
RCD would be a simple solution, but we have a VERY limited budget at the moment.

The wiring is in plastic trunking on a floating ceiling, so not much to bond up there with a good connection.

I'm thinking linking all those earths is the cheapest, easiest solution.

I will see how that goes then, if problems, work out what to do next.
 
RCD would be a simple solution, but we have a VERY limited budget at the moment.

The wiring is in plastic trunking on a floating ceiling, so not much to bond up there with a good connection.

I'm thinking linking all those earths is the cheapest, easiest solution.

I will see how that goes then, if problems, work out what to do next.
 
RCD would be a simple solution, but we have a VERY limited budget at the moment.

The wiring is in plastic trunking on a floating ceiling, so not much to bond up there with a good connection.

I'm thinking linking all those earths is the cheapest, easiest solution.

I will see how that goes then, if problems, work out what to do next.

Like using larger CPC's from the DB!! ...lol!!!
 
We are very limited on space, and that would be 1 hell of a job. Linking the CPCs will have a far greater effect for less time and materials.

The last thing I want to do is be dragging in huge amounts of wire down 20mm copex.

Hopefully yes!!, but my reply was based on your comment....
will see how that goes then, if problems, work out what to do next.
In other words, if it doesn't provide the necessary results!! lol!!

 

Reply to Zs a little out, what can I do to fix it? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top