its what they teach you these days and reason i said that is because we were talking about the exact subject on monday. not always an option for new circuit or breaker device to be reduced, thats all folks!!!!!!!!!!!!!!!
 
had a similar problem to be solved in the 2391 practical.
Zs value was too high for ADS.
Assuming the system is TN-C-S
Number of solutions:
Check R1 +R2 equals what you would expect using the resistances/m as shown in OSG page 166. Could indicate poor connections
Check the MCB type as it could be a C type where it may be possible to have a B type depending on what the load type is. B types have a higher max Zs value compared to C's
Could reduce the length of the circuit
Could use cables for the circuit having a larger csa
 
and if all else fails there is always the fast track course 7 weeks learning how to lie through your teeth, become a .......... politician, lawyer, estate agent, salesman, banker, care home manager, any manager, sure there's more.......
 

Reply to Zs fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
715
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
970

Similar threads

  • Question
Agreed, loss of N further down the network can give wildly changeable voltages If it is tied to earth, then that will go up and down too.
Replies
3
Views
495
For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
506

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top