I was gona reply to this before i left for work, but gave up. But back home now having a beer.
Anyway I totally agree with E54 here.
So you have 3 options.
1 Decrease the Zs readings of the circuit by increasing the earth size or decreasing its resistance.
2 change MCB's to Type C, and hopefully your readings will then comply, im wondering why type D was installed, but without looking at the installation then its a guess.
3 disconect the Earth and make the outside stuff a distribution circuit and create a TT area where the max is then 1667.
But if you go with option 3 then as Im sure E54 will say Don't use a stick as a rod as all they are good for is poking apprentices that fall asleep...
Ps Ive had a beer so it may sound a pile of *****what Ive said. :)
Reply to Zs on a RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...