i=p/u
Northern Ireland
What is the point in carrying out zs on TT system other than verifying a loop.
We got an Ra of 14.8 but when all bonding is in place it comes down to 1.9 ohms for most circuits zs results. I just don't see the point if rcd protected .
Reply to Zs on TT in the UK Electrical Forum area at ElectriciansForums.net
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
OLDBOY
O
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...