Arms
What is the point in carrying out zs on TT system other than verifying a loop.
We got an Ra of 14.8 but when all bonding is in place it comes down to 1.9 ohms for most circuits zs results. I just don't see the point if rcd protected .
 
i=p/u, while I agree that the values are somewhat irrelevant as regards disconnection times, what Sintra and hawkmoon are trying to point out is that without the "live" Zs test the connections at the ocpd and RCD and the devices themselves are completely missed out with just Ra & R1+R2 tests.
 
i see i=p/u is drowning in a pool full of his own thread fail.........

here , let me help.....

ring.png
 