i=p/u
What is the point in carrying out zs on TT system other than verifying a loop.
We got an Ra of 14.8 but when all bonding is in place it comes down to 1.9 ohms for most circuits zs results. I just don't see the point if rcd protected .
I was going to write a silly answer but I gave up because I couldn't make it as silly as the question. Can you rephrase?
I read it as: Why test Zs on a system where the Ze is much higher than the Zdb? Or maybe: 'Why test Zs when the results are going to be high but not too high.' Either way it's pretty wacky.
This one is a serious contender for 'thread of the week' award, I've had tears rolling down my face whilst reading it.
I assume Mr I=PU is asking why is the Zs relevant if you know the Ra is good enough to meet the required earth impedance on its own without the assistance of parallel paths.
Okay, I'm going to let the English who apparently 'are slow' and allegedly 'on the ale' sort this one out ;)
Don't forget that we are all apparently Gay as well ! :shocked3:
Edit; According to another thread at the moment that is !
looks like i`v missed a few good opportunities this evening to have a go..
got called out to a faultfind which turned out to be several neutral-earth faults...
and yep....the RCD was tripping...
it aint now though.....;)
No glen not have a good go, no no no , support what I am saying.
if you have ze of 14 ohms what is the point of doing zs test , as you know your readings are to high for protective device already.
Brains just ain't your friend last two days guys , AAA?
Assuming this is not a wind up...
Forget the fact this is TT and rethink what a Zs test is for
On a 6A lighting circuit max zs is 6 odd ohms to disconnect a fault within specified time . On this TT system with 100mA rcd, our Ze is14 ohms soothe breaker won't trip within time, so relying in rcd.. Oh my god