Morning, just checking a lighting circuit on a house, I have the main earth disconnected and still get a zs reading of 2.2 ohms. No evidence of an earth spike and bonding goes direct to henley block.

Any suggestions why this could happen??
 
I have also disconnected the main earth to demonstrate to apprentices how parallel earths can appear to drag down the Ze or Zs readings of a TT installation.
I have also disconnected the main neutral to demonstrate how this can be dangerous..
 
Whatever the justification for energising some hypothetical system with the earth disconnected for demonstration or analytical purposes, the OP had a specific task in hand which was to trace a connection to a section of CPC that did not seem to start at the origin. As such, it's a simple continuity test to the MET, other CPCs or mass of earth, that does not require the system to be energised to trace. There is no justification here to work with the system energised.
 
did you finally find the root cause of your problem ? if yes i would appreciate you share it. i have the same. w / wo main Earth wire connected i read same Zs 1.5 ohms. ( TT system) . thank you
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
 
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenon
 

Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
833
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
884
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top