J

james king

any ideals on why it said trip i have a megger mft 1553. testing between live earth and nutral with lead test. but dont work lol

any help will be great thanks .
 
probably because your putting a fault current of around 20amps on a 6a breaker either step up the breaker just for the test or use r1+r2+ze
 
no i use a no trip witch put i think 10amps thru it ok il just do the maths lol thnaks for ur help.. also i take it ur a expericnece spark can u help with a few more testing Qs??
 
well u say that... some people do not.

all it was is i tested a rcd to day i got a reading of 18.1ms i think on 1sec and reading of 4.9ms on x5 can u help with the mas tripping times?
 
RE: Zs trip reading - ensure you have a good connection on the contacts when carrying out the test. If any of your probes lose contact for a moment the meter will read trip. If you are using a croc clip to connect the earth test lead, make sure this is clamping firmly.
 
probably because your putting a fault current of around 20amps on a 6a breaker either step up the breaker just for the test or use r1+r2+ze

Never EVER use a higher rated MCB. If your meter doesn't have a No Trip EFLI setting (which his Megger MFT1553 DOES have) then it should be calculated (i.e. Zs=Ze+(R1+R2)).

no i use a no trip witch put i think 10amps thru it ok il just do the maths lol thnaks for ur help.. also i take it ur a expericnece spark can u help with a few more testing Qs??

Loop test is around 26A I think. No trip is around 15mA (not 10A).
 
Last edited:
I have to agree with JulianC, I have found on many occasions that if the probes have a bad connection that the meter shows fail..
 
I've had it also many times, apparantly randomly, it's getting to be a bit of a P.I.T.A. I've always made sure the connections are good, and still it randomly occurs. I do the Zs by calc when it does happen now.

I must admit that I wasn't aware that a split second disconnect could lose the test though.
 
cheers for that every one just bit strage had it happen few time and wondered what was going on i use my cals to do Zs but stil wanted to no y it happend cheers
 
As previously mentioned ,during a no-trip test, a momentary break in either the neutral or earth connection will cause "trp" to be displayed as the MFT assumes an interruption in supply.

A poor connection in the circuit cpc can also cause this issue.

Regards

Megger TSG
 

Reply to Zs test at last lighting point reading "trip:" in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
378
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top