please can anyone help.zs on lighting useing 3-leads .where do they go im useing megger mft1553.
 
lenny one more question pls.I HAVE 3-LEADS COMEING OUT FROM MY MEGGER,looking at the one way switch for the lighting i can see brown-com switchwire-L2 and earth CNNECTED TO THE META LBOX,MY Q IS WHERE DO THE 3-LEADS FROM THE MEGGER GO TO.
 
Sorry mate, for a 3 lead test with the megger you need to test at a point on the circuit that has a neutral ie. the light fitting or rose.
The green lead connects to the earth the black lead connects to the neutral and the red lead connects to the switched line.
 
Sintra thanks for that information,so you saying you cant do zs from a one way switch,pls correct me if i understand you wrong
 
As my esteemed colleague has said in order for 'no trip' test with an MFT you need a neutral present. With only L&E present you can only use the high current loop test function.

Again Page 4 of the link I posted shows this.
 
Not on a circuit that is RCD protected and has no neutral in the switch. For an RCD protected circuit you have to use the no trip setting on the meter and 3 leads which means you need a connection to neutral.

If the circuit is not RCD protected then use the high setting with 2 leads (red & green) connected to line and cpc in this case it could be tested at the switch.
 

Reply to Zs test at last lighting point reading "trip:" in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
761
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top