Zs to high | Page 2 | on ElectriciansForums
Discuss Zs to high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
do you mean periodic inspection
and not periodic inspection and test as it says in gn3
Periodic inspection and testing would be a satisfactory answer. You have a Periodic Inspection Report rather than a Periodic Inspection and Testing Report so I can't see anything wrong with periodic inspection either.
thanks risteard mate
only realized other day i was writing periodic inspection report doh
could you tell me two formulae for ZS is it
ZS = ZE+(R1+R2)
ans ZS = ZE + mohm/m x mf x length divided by 1000
and the Min value you reckon is 1Mohm
what page of regs as ive looked and only where it says 1Mohm is as i stated in earlier post for surge protective devices left connected at 250v d.c. 1Mohm min
and selv to band II
and selv to band II
Had a flick through and can't find it. Will have a look later for you.
Regards,
R.
Reply to Zs to high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...