max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)

What gives you that idea??

Zs = Uo ÷ Ia is basic ohms law (R = V ÷ I).

Zs = Earth fault loop impedance -- Uo = Nominal voltage -- Ia = Current causing operation of the protective device in the required time

The 0.8 is a rule of thumb. The max Zs values in BS 7671 are at a cable operating temperature of 70°C but the cable won't be at that temperature when you take a Zs measurement, so you multiply the values in the BRB by 0.8 to account for the reduced temperature of the cable.

Ia is taken from the time/current characteristics graphs/tables in Appendix 3 of the BRB.

That's a great formula but would it still apply to bs88 fuses?

So yes, it does apply to BS 88 fuses. It's just easier to work out for 60898 and 61009 breakers because it's just 5 x In (type B), 10 x In (type C) and 20 x In (type D).
 
Last edited by a moderator:
Soooo - Smiffy is right then.
So yes, it does apply to BS 88 fuses.
Obviously, Ohm's law applies to everything but -
It's just easier to work out for 60898 and 61009 breakers because it's just 5 x In (type B), 10 x In (type C) and 20 x In (type D).
...there is no one value which applies throughout the amperage range of BS88s to calculate the maximum Zs for each.
 
Soooo - Smiffy is right then.
Obviously, Ohm's law applies to everything but -...there is no one value which applies throughout the amperage range of BS88s to calculate the maximum Zs for each.

No. What Smiffy said is that Zs = (Uo ÷ Ia) x 0.8 cannot be used for anything but 60898 and 61009 breakers.

max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)

Uo ÷ Ia is how max Zs values are calculated no matter what the protective device.

Have a look at the time/current graph for BS 88 fuses on page 247 of the BRB. Let's say you have a 32A fuse.

For a disconnection time of 0.4s you need a fault current of 220A. Zs = Uo ÷ Ia (230V ÷ 220A = 1.04Ω). Now compare this with the value in Table 41.2 on page 48.

You then multiply this value by 0.8 to account for the reduced temperature of the cable -- 1.04 x 0.8 = 0.83Ω. This is your maximum measured value.
 
Yes, I know but smiffy's thread is about the fact that you don't need the graphs for 60898s because the relationship between Ia and In is linear,

i.e. 5, 10, 20 for B, C, D respectively.

This is not the case with BS88s and, indeed, other fuses.
 
Yes, I know but smiffy's thread is about the fact that you don't need the graphs for 60898s because the relationship between Ia and In is linear,

i.e. 5, 10, 20 for B, C, D respectively.

This is not the case with BS88s and, indeed, other fuses.

He didn't say anything about not needing the graphs.

What he said in post #75 was the formula for calculating max Zs "only works for B C D mcbs 60898 rcbos 61009". This simply isn't true.
 
Last edited by a moderator:
max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)
Jud - you are strictly correct but post #75 was in reply to another post and I, at least, think it quite obvious that he is referring to his discovery/realisation that the 5, 10, 20 only works with 60898s.

Also, as you can see he does refer to 'without looking it up' or as I put it 'needing the graphs'.

I just got the impression that you were 'raining on his parade' when he wasn't really wrong if read in conjunction with his previous post.


Edit -substituted I for you
 
Last edited by a moderator:
Jud - you are strictly correct but post #75 was in reply to another post and I, at least, think it quite obvious that he is referring to his discovery/realisation that the 5, 10, 20 only works with 60898s.

Also, as you can see he does refer to 'without looking it up' or as I put it 'needing the graphs'.

I just got the impression that you were 'raining on his parade' when he wasn't really wrong if read in conjunction with his previous post.


Edit -substituted I for you

I didn't intend to rain on his parade. His previous post regarding 60898 and 61009 breakers was bang on the money.

I was replying soley to post #75, which is why I quoted it. SimpleSimon asked if the formula also applied to BS 88 fuses, to which Smiffy replied...

max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)
 

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
342

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top