why are osg tables 80% of bs7671?

When you do the Zs test the cable temperature will be around 20°C. The tables in the regs are the max Zs values when the cable temperature is 70°C.

As resistance increases as cables get hotter (0.4% per °C) you need to adjust the max Zs value for the lower temperature of the cable.

e.g The difference between 20°C and 70°C is 50 so the calculation would be 50 x 0.4% = 20% so the corrected max Zs values for 20°C would be 20% less than the ones for 70°C.

Hope that makes sense ;)
 
malcolm, could you clarify your last post please. say for a 32AMCB, the max. allowable value of Zs is 1.16, what you are saying is, if the circuit is RCD protected you enter 1667, not 1.16?
 
That's exactly right, many people incorrectly assume this is just for TT systems.
 
so, one advantage of the 17th is, with everything now on RCD ( well almost), we don't have to remember all those max. Zsvalues for different MCBs. every cloud has a silver spoon!
 
RCD/RCBO circuits will have the Zs part of the form filled in as 1667 as that is the "Zs" as such for the circuit.

On domestic the chances are that as the board that is fitted will be a dual board then you also have overload protection by MCB and that circuit will have your Zs, and you will enter the Zs results. A lot of argument is now happening that even on dual boards you can fill the Zs for each circuit as 1667 as all circuits are RCD protected. IMO in a few years once we are all use to this we will all fill the schedule of resutls with RCD protection as 1667. I have to admit until recently I use to fill the Zs part in for each circuit as measured but I will start doing it the 1667 method.

Obviously on PIR's for older installtions, and installtions not needing RCD protection you will still do Zs as normal.
 
even so, still put in the measured Zs in it's column, but max. as 1667.
 
That's exactly right, many people incorrectly assume this is just for TT systems.

I was told recently by a NIC man that TT is 1667 and TN is 1.6 Kohm !!! After I stopped laughing at him he told me that as he was an assessor that was what should be written
 
Well that's your answer Malcolm, the Lord hath spoken!

And on the seventh day, the NICEIC wrote the regulations!
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.

If the maximum Zs value for a circuit in a TN system cannot be met, the circuit may be protected by a 30ma RCD. 531.3.1
 
Last edited by a moderator:

Reply to the thread, titled "Zs values?" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zs values?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
83

Thread Tags

Advert

Thread statistics

Created
bs7671,
Last reply from
Dan,
Replies
83
Views
15,684

Advert

Back
Top