why are osg tables 80% of bs7671?

When you do the Zs test the cable temperature will be around 20°C. The tables in the regs are the max Zs values when the cable temperature is 70°C.

As resistance increases as cables get hotter (0.4% per °C) you need to adjust the max Zs value for the lower temperature of the cable.

e.g The difference between 20°C and 70°C is 50 so the calculation would be 50 x 0.4% = 20% so the corrected max Zs values for 20°C would be 20% less than the ones for 70°C.

Hope that makes sense ;)
 
malcolm, could you clarify your last post please. say for a 32AMCB, the max. allowable value of Zs is 1.16, what you are saying is, if the circuit is RCD protected you enter 1667, not 1.16?
 
That's exactly right, many people incorrectly assume this is just for TT systems.
 
so, one advantage of the 17th is, with everything now on RCD ( well almost), we don't have to remember all those max. Zsvalues for different MCBs. every cloud has a silver spoon!
 
RCD/RCBO circuits will have the Zs part of the form filled in as 1667 as that is the "Zs" as such for the circuit.

On domestic the chances are that as the board that is fitted will be a dual board then you also have overload protection by MCB and that circuit will have your Zs, and you will enter the Zs results. A lot of argument is now happening that even on dual boards you can fill the Zs for each circuit as 1667 as all circuits are RCD protected. IMO in a few years once we are all use to this we will all fill the schedule of resutls with RCD protection as 1667. I have to admit until recently I use to fill the Zs part in for each circuit as measured but I will start doing it the 1667 method.

Obviously on PIR's for older installtions, and installtions not needing RCD protection you will still do Zs as normal.
 
Well that's your answer Malcolm, the Lord hath spoken!

And on the seventh day, the NICEIC wrote the regulations!
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.

If the maximum Zs value for a circuit in a TN system cannot be met, the circuit may be protected by a 30ma RCD. 531.3.1
 
Last edited:

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
342

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top