why are osg tables 80% of bs7671?
When you do the Zs test the cable temperature will be around 20°C. The tables in the regs are the max Zs values when the cable temperature is 70°C.
As resistance increases as cables get hotter (0.4% per °C) you need to adjust the max Zs value for the lower temperature of the cable.
e.g The difference between 20°C and 70°C is 50 so the calculation would be 50 x 0.4% = 20% so the corrected max Zs values for 20°C would be 20% less than the ones for 70°C.