A common source of misunderstanding is that of either specifying or measuring values of ELI where the circuit also has an RCD fitted. ELI measurement under these circumstances is a futile excercise.
The circuit will have been checked for continuity, and this is all that is needed together with, of course, functional checks of the RCD.
This criterion satisfies requirements for automatic disconnection.
The subject is somewhat confused by the inclusion of RCBO's in table 41.3 and for clarification, circuits with RCBO's do not need to meet the specified ELI values.
The circuit will have been checked for continuity, and this is all that is needed together with, of course, functional checks of the RCD.
This criterion satisfies requirements for automatic disconnection.
The subject is somewhat confused by the inclusion of RCBO's in table 41.3 and for clarification, circuits with RCBO's do not need to meet the specified ELI values.