can zs readings be taken without cheacking r1+r2 on periodic testing
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
There could be quite a lot of reasons you can not take an R1 + R2 reading on a EICR
Unable to isolate a circuit in a commercial/ industrial environment
Hi Bay lighting circuit
Safety Services
They spring to mind in a few seconds. So again there is no reason you need to do a R1 + R2 test on an EICR to record a Zs value
Surely if you can measure Ze at board (or obtain by enquiry), but as you say for some reason can't turn off to do dead testing, you can still measure your Zs at the outlets which you do live anyway.
Then, assuming that's good, (R1 + R2) = Zs - Ze.
If you're allowed to put one figure down obtained 'by calculation' why not another? As long as you state that.