The sequence of testing is for safety reason, so I would say not as you need to verify the earth path you are testing is back to the earth of the DB being tested
 
You can put as little or as much information down as you like, As long as the reasons why are included. This must be accepted by the client which is why page 1 includes this information but why would you want to not do half the testing.
 
There could be quite a lot of reasons you can not take an R1 + R2 reading on a EICR

Unable to isolate a circuit in a commercial/ industrial environment
Hi Bay lighting circuit
Safety Services

They spring to mind in a few seconds. So again there is no reason you need to do a R1 + R2 test on an EICR to record a Zs value
 
There could be quite a lot of reasons you can not take an R1 + R2 reading on a EICR

Unable to isolate a circuit in a commercial/ industrial environment
Hi Bay lighting circuit
Safety Services

They spring to mind in a few seconds. So again there is no reason you need to do a R1 + R2 test on an EICR to record a Zs value

Totally see where your coming from but if site conditions dictate you cant obtain R1 + R2 then you would have to clarify you cant obtain your Zs
 
Surely if you can measure Ze at board (or obtain by enquiry), but as you say for some reason can't turn off to do dead testing, you can still measure your Zs at the outlets which you do live anyway.
Then, assuming that's good, (R1 + R2) = Zs - Ze.
If you're allowed to put one figure down obtained 'by calculation' why not another? As long as you state that.
 
Surely if you can measure Ze at board (or obtain by enquiry), but as you say for some reason can't turn off to do dead testing, you can still measure your Zs at the outlets which you do live anyway.
Then, assuming that's good, (R1 + R2) = Zs - Ze.
If you're allowed to put one figure down obtained 'by calculation' why not another? As long as you state that.

Sounds right, but in GN3 they state you cant rework that figure with that calc, would be to easy but with all the paralel paths as it is a live circuit with bonds in place
 
If you have a previous PIR or cert available when carrying out a EICR,and that cert gives R1+R2 and Zs readings,there really is no need to carry out further R1+R2 tests,which can be time consuming and disruptive. If your Zs test results are identical or at least close to the results on the previous cert,it is reasonable to assume the R1+R2 readings will be the same as well......obviously this approach should be explained on the new cert.
 

Reply to ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top