Discuss Adding another circuit ! in the UK Electrical Forum area at ElectriciansForums.net
Have a 63A RCD 5 Way box, with a 45A MCB, feds by 16mm2 tails, this in then feeding into a isolator via 10mm2 T&E, that then supplies the feed to a 6.5KW heater that is used prob once a month for 10 min intervals max.
Question: I have a spare 63A RCB + 20A MCB box, Can I take another feed from the input of the 63A isolator to feed that, then that would feed into the next building to feed a compressor, some sockets etc via 4mm2 T&E ?.
cheers
Spike
cheers
Spike
Lots of pictures may help of each item and where the 16mm tails originates along with what else it feeds.
Lots of pictures may help of each item and where the 16mm tails originates along with what else it .
To be honest I'm doubting we will reach the threshold of information required to say for certain "yes, this is safe, go ahead". It's not changing a light fitting, it's a very general question about adding distribution circuits, and I don't think we should be signing off the design over the internet.
Very true, but I wouldn't mind seeing the pics
Previous posts of the OP related to a 3ph TT farm.
What I can understand is he wants to come off the supply side of a cu mainswitch, run an swa to another building to feed another cu.
If there is no space to give it an mcb within the board, I would suggest splitting before the first cu with Henley’s, an isolator and fusing the swa down.
The “5 way rcd box” is irrelevant. It only suggests the entire circuit is rcd protected at source and is on a 45A OCPD.
I know what you mean, but the 16mm tails could mean 60A supplier fuse, and max demand of the whole lot might be a consideration.
Indeed.
Sounds as though the only extra load is a 20 and a 6 breaker… could just be a light and a socket… or could just as likely be a dozen lights and any number of sockets… but max 26A
The only issue might be during the 10 minutes that the big heater is on.
Reading it again, it also seems like he’s running this new part in t&e…. Which is wholly unsuitable.
Reply to Adding another circuit ! in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Due to an increase in load for a subman, I now need 2 phases for an outbuilding. Original design was 63a supply, but now an electric shower and...
The ongoing kitchen refit..... I have chased and fitted 10mm T&E from the cooker outlet to the isolator switch and up into the loft. I have 4...
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
