3-phase

  1. D

    Is it 3-phase?

    Chaps, can you tell me if the supply head in the picture attached is three phase? Thanks!
  2. R

    3-phase thyristor control

    I want to try and replace the standard relays on our holding pots that are being kept hot by elements. I want to use thyristors instead, but i'm not sure what the best way would be. I would like to implement zero crossing control. So when 1 is fired in the forward dirction, 2 and 3 should be 1/3...
  3. W

    No 3-Phase Connection - Building Overcapacity!

    Couple of weeks ago I signed a lease on an industrial unit (all 25 units in the building are 'wired for 3-phase'). Although the unit had a single phase CU the wiring was there for 3Ph. Spent the last week installing a 24way DB, sockets, isolators etc. etc. etc., got it all checked and...
  4. D

    3-phase calc

    quick question: a 3-phase lift rated at 2.2kw 6.4 amp doesn't seem to add up for me?
  5. F

    3-Phase 415V supply. How many circuits?!?

    Hi! I have recently changed my job and my employer has asked me to survey the existing electrical system. The main incomer is 100A 415V 3-phase and neutral and each phase and neutral is attached to a separate CU. This is how is breaks down:- L1+N= (100A CU) Handdriers in toilets, lighting...
  6. sparks1234

    3-phase

    If you are running a single phase board in a commercial premesis, its the only board in the place, but the incomer is 3-phase with a 3-phase meter but only single phase leaving the meter, would you still double the KA?
  7. P

    Single & 3-Phase Voltage in The UK

    Hi all, Just a quick question on single phase and 3-phase voltage. Do The UK use 240V Single Phase and 415V 3-Phase?
  8. B

    3-phase to 1 phase?

    I've got a boat, and often connect to shore-power using a 230V IEC blue 16A plug like this: A lot of places now have IEC sockets that take a 415V 3P+E red plug like this: Can you get a converter, I'm guessing it would be a transformer?
  9. M

    Cannot get 3-phase - problem?

    I have the following: Extension Ring 32A Up Ring 1 32A Up Ring 2 32A Down Ring 1 32A Down Ring 2 32A Kitchen 1 Ring 32A Kitchen 2 Ring 32A cooker 1 32A Cooker 2 32A Shower 16A Up Lights 1 6A Up Lights 2 6A Up lights 3 6A Down Lights 1 6A Down Lights 2 6A Down Lights 3 6A Smoke...
  10. S

    Meggering of 3-phase Synchonous Generator

    For phase to phase Meggering of 3-phase Synchonous Generator, we have to open its flexible links (between phases) & its star point. We then connect Megger's positive lead to phase (which we want to Megger) & we short remaining two phases with ground?(& connect megger's negative lead to it) Why...
  11. S

    Differential Protection testing of a 3-phase transformer

    For Differential protection testing of a three phase Power T/F using secondary injection test set, how do we know the correct value of current to pe applied(value at which relay picks up)? Does OEM provide these values in Instruction manual or Electrical Engineers calculate these values...
  12. W

    3-phase wiring at home

    Hi guys, I've just been given a date for EDF to come and connect 3-phase supply to my garage at home (I'm starting my own business and unfortunately the control cabinet I'm designing needs 415v 3p, so to hold off renting a unit I thought I'd power-up and test the machine at home). I've sourced...
  13. C

    3-Phase Generator Question

    Hi all, Got an interesting generator related issue here………………. I’m currently helping a friend with a 100KVA geni and I’m after some advice. I’m trying to work out what the maximum current draw would be………….. So if O\P Amps = KVA / (O\P Volt / 1000) = 100/(240/1000) = 416.66 Amps But as...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc