I've managed to mainly fix a Megger 1502 MFT that was so far out of calibration it got laughed out of a tester day.
I have high current loop. rcd test currents, and low resistance within spec now. (I can share more info about this process separately if anyone's interested, it's been an interesting learning curve).
IR results are just about within +-2% +-2 digits. To get them more accurate I need a 5M resistor with lower than 5% tolerance. I struggled to find anything cheap and these results were obtained using a 3M and 2M in series, they both have 5% tolerance and overall it's not quite good enough.
So the first easier question is any recommendations for better resistor accuracy, hopefully without spending a small fortune. I'm wondering if adding a trim pot is a good idea.
The 2nd question is more complex and regards the low-trip loop calibration which is the last real hurdle and may prove to be the brick wall I hit.
Part of the test passes 25A current between Live and Neutral as a basis for further maths.
Part of the calibration involves adding 10 ohms to the Neutral path and storing the result, and adding 10 ohms to the earth path and storing the result. No problem so far.
But then adding 10 ohm load to the Live path....On the face of it this would seem to need a resistor rated at 5.29kw ?! Or am I getting something basic very wrong? Obviously this is lethal enough anyway and I will admit defeat and draw stumps if I can't be sure what is required here.
Thanks for any thoughts.
Excerpt from the service manual: