Currently reading:
RCBO tests
Discuss RCBO tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Anyone an idea why an RCBO measures >40ms on a 5x test on the second half of the sine wave but all other tests are within requirements? Sorry, it's not a single RCBO, there's 2 RCBOs in this board and both have similar results leading me to think not a faulty RCBO but an issue further upstream somewhere. Continuity, IR, Zs all textbook.
Trip times are something like 48ms on 1x, 28ms 5x on first half and >40ms second half 5 for both devices. No other RCBOs in the board but a different, adjacent board's RCBO tests fine.
Nothing for certain but a technical thought ,since DC
sensitive RCBO's have been mentioned !
Are there any DC powered appliances - PC Power supplies,inverter washing machines present.
(Wacky idea, each half cycle has a polarity , Are we looking at a pulsed DC leak de sensitizing 1 polarity ?)...
I may just be a rabied dog barking up a theoretic tree ... Faults do come in batches .
(though does feel like a feature of install / or test gear brand mix)
rolyberkin was having similar problems with a 32A
Lewden.
RCBO Test data - 40 milliseconds
I Have my doubts at times with MFT
software -"recognising test results" that are not common yet !
With the pods the manufacturer advises that You have to remove the wire from the terminal and just insert the probe into the terminal.
The only probe I’ve managed to inert are the very fine ones that screw or insert onto the tests lead
Unsure if this is 100% correct