Thats far to close, a type c 16 will allow LOTS more than 17.5 amps through it ( ok i forgot how much more )for a short duration of time, if your cable max is 17.5......... I wouldnt sleep at night.
I'm allowed 6% voltage drop. 6% of 230 = 13.8volts.
Thanks. So from your formulea I need 10.2 amps per phase (call it 11). Now have I got this correct:
at 11 amps = 1.2545 volts/amp
at 40 meters = 1.2545 / 40 = 0.0313636 volts / amp/ meter = 31 mV/A/M
and according to table 4D2B col 4 this can be achieved with 1.5mm cable.
1.5mm cable run using Reference Method C (clipped direct) can support 17.5 A. So I install a 16A 3 Phase type C MCB and off I go. Right?
Thanks for any comments.
Close enough for me Steve! 4.0mm.Also, an alternative way to work it out is to divide by 3 then divide by 230.
Eg 12kW / 3 = 4kW 4kW / 230 = 17.39A
using the I=P/(Vx1.732) equation 12000/(400x1.732) = 17.32A
Ok, you don't get the identical answer, but it's as near as damnit.
However, I normally use the 1.732 method.
Well I came in to appologise for the way I expressed somthing earlier today. But since half the posts relevant to this topic have been lost I'm afraid I can't. Sorry about that.
MCB curves.
Type B 5 Times overload current rating for about 30 minutes.
Type C 10 times and type D 20 times.
Cheers............Howard![]()