Watts to Amps
For single phase its easy Amps = Watts/Volts.
Is it as easy for 3 phase?
Amps = Watts/Volts/3 per phase.
or is there a root 2 in their somewhere?
I need to know to calc the voltage drop along the supply.
Thanks in advance for any offers.
Thanks. So from your formulea I need 10.2 amps per phase (call it 11). Now have I got this correct:
I'm allowed 6% voltage drop. 6% of 230 = 13.8volts.
at 11 amps = 1.2545 volts/amp
at 40 meters = 1.2545 / 40 = 0.0313636 volts / amp/ meter = 31 mV/A/M
and according to table 4D2B col 4 this can be achieved with 1.5mm cable.
1.5mm cable run using Reference Method C (clipped direct) can support 17.5 A. So I install a 16A 3 Phase type C MCB and off I go. Right?
Thanks for any comments.
Thats far to close, a type c 16 will allow LOTS more than 17.5 amps through it ( ok i forgot how much more )for a short duration of time, if your cable max is 17.5......... I wouldnt sleep at night.
MCB curves.
Type B 5 Times overload current rating for about 30 minutes.
Type C 10 times and type D 20 times.
Cheers............Howard;)
Double check your volt drop values
5% for power
3% for light
3% for lights because of the high frequency stuff being useed.
You need to write in to the IET - You've put a whole new spin on cable selection.:D
I don't think you're supposed to select your cable based on volt-drop.
I thought it went something like this (briefly):
You take the design current and select your cable, taking into account the installation/reference method.
Then, having selected your cable, you select your protective device.
Then, take your design current and cable length and volt drop rating (mV/A/m) and calculate your volt drop - and compare this to what is allowed.
Also, an alternative way to work it out is to divide by 3 then divide by 230.
Eg 12kW / 3 = 4kW 4kW / 230 = 17.39A
using the I=P/(Vx1.732) equation 12000/(400x1.732) = 17.32A
Ok, you don't get the identical answer, but it's as near as damnit.
However, I normally use the 1.732 method.
Close enough for me Steve! 4.0mm.
Well I came in to appologise for the way I expressed somthing earlier today. But since half the posts relevant to this topic have been lost I'm afraid I can't. Sorry about that.
There seems to be posts going missing everywhere at the moment.......I'll have a look into it.:)
MCB curves.
Are you completely sure that these MCB's will hold with that kind of overcurrent? As far as I was aware, those overcurrents are for an instantaneous trip... Have a look at your trip curves at the back of your BRB.
sirkits origional post is correct it acounts for inrush current such as a motor starting ect or high frequency stuff. They will take the much larger inrush current for a longer period but not indeffinatly.
NoSparks,
pevvers,
TrueNAS JBOD Storage Server