an mccb main switch then mcb's or mccb's feeding sub boards.
when the shower/sockets/lights trip it doesnt trip every other mcb does it, same thing
Depends on the magnitude of the fault on the sub-DB circuit Shanky, with MCBs you only get partial discrimination at best, as Davesparks pointed out earlier HRC fuses > MCBs provide better discrimination.
what im saying though is the intake would be into a mainswitch that wouldnt trip then wither mcb's,mccb's idealy for each board.
they are all split off from the same point so how can the others trip honestly.
if the supply to all three was fed from the same mcb etc i could understand where you are coming from
I agree with you here ^^, I thought you were talking about feeding the sub-boards from an MCB, my bad :35: lol
fair enough but im sure you can still buy bs88 boards.
or mccb's
Yes BS88 boards are still available and have their place in installations. MEM excel boards spring to mind, but they don't have main switches so would put us back at square 1
No it's not the same thing, you suggested installing a DB and feeding sub mains from MCBs in that DB.
That puts the final circuit MCBs on series with the distribution circuit MCB, this will may not discriminate in the event of a fault on the final circuit.
That is what I thought I was replying to earlier, tis Friday night though ;)
the installation is a 3 phase incoming, however only one the phases used which goes into a henly block then splits into 3.
so best practise would be to place the isolator before the henly block so the main switch covers the whole installtion.
oh and they reasons why the main switch cant be a RCD switch.
Do you really need to ask this??
Read 314.1 in the BGB then have a think why you shouldn't fit a RCD main switch on a TN system.
potentially if we had nuisance triping it could be a killer for this type of business. so rcd protection as a main switch is a no no. RCBO protection for socket circuits is needed so only that circuit in question would disconnect instead of whole supply
North
main switch question
paulthemagpie,
paulthemagpie,
