Is TNS permitted on caravan site? I always thought you could use as TNS as supply cable then TT each pitch, spark I’m working with says you can use TNS all way through if ZS is acceptable
Thanks
 
ESQCR are does NOT allow pme conditions to a static caravan! It does allow it for buildings on parks, not the vans themselves
Here is a quote from BS7430 (earthing Code of Practice):

"NOTE Residential caravans which are not normally intended to be moved from a caravan park are regarded as permanent buildings."
 
Here we go.
Just because the supply to the installation is TN-S, doesn’t mean PME conditions do not apply.
It’s why BS7671 states “where PME conditions apply”, rather than saying “where the earthing system is TN-C-S”.

Yes ESQCR does prohibit the use of PME for Caravan pitches.
However it does not prohibit the use of PME for static Caravans or for other permanent structures on Caravan sites.

If it is as you put it ‘A TN-S with PME conditions’ then it is not a TB-S is it?

It is up the the DNO to ensure their supply arrangement is vlear nit for us to go around asking questions.
 
Regardless, BS7671 is clear that a PME cannot be used.
No, it’s not.
From BS7671 Definitions:
Caravan. A trailer leisure accommodation vehicle, used for touring, designed to meet the requirements for the construction and use of road vehicles (see also definitions of Motor caravan and Leisure accommodation vehicle).
 
If it is as you put it ‘A TN-S with PME conditions’ then it is not a TN-S is it?

It is up the the DNO to ensure their supply arrangement is clear not for us to go around asking questions.
If it’s not TN-S then fine.
Won’t ever need a DNO to come out and convert a TN-S supply to TN-C-S.

I won’t bother pointing out, that BS7671 states we can obtain information regarding the characteristics of a supply by enquiry.
Or that ESQCR requires DNOs to supply such information upon request.
 
Like I said BS7671 dors not so if you do you are not following BS7671. Very simple.
Actually, it does:
708.411.4 TN system
The Electricity Safety, Quality and Continuity Regulations (ESQCR) prohibit the connection of a PME earthing facility to any metalwork in a leisure accommodation vehicle (including a caravan).
This does not preclude the use of a PME earthing facility as the means of earthing for other purposes, such as to the installations of permanent buildings.
NOTE: The requirements of other sections of Part 7 may also apply.
 
Actually, it does:
708.411.4 TN system
The Electricity Safety, Quality and Continuity Regulations (ESQCR) prohibit the connection of a PME earthing facility to any metalwork in a leisure accommodation vehicle (including a caravan).
This does not preclude the use of a PME earthing facility as the means of earthing for other purposes, such as to the installations of permanent buildings.
NOTE: The requirements of other sections of Part 7 may also apply.

So what i said earlier then!!!
 
So what i said earlier then!!!
No not really.
You said ESQCR does NOT allow PME conditions to a static caravan! It does allow it for buildings on parks, not the vans themselves”
BS7671 does not define a static caravan as being a caravan.
It only defines touring caravans as being caravans.
Also, BS7430 which is the earthing COP used by the DNO, considers static caravans as being permanent buildings.

That being said, it doesn’t preclude the DNO from refusing a PME connection to a static caravan, on safety grounds, due to the metal skin.

Of course, all this has nothing to do with the OP’s question regarding whether TN-S can be used throughout a caravan site.
The simple answer being yes.
The proviso being that it should be determined first, whether PME conditions apply.
If PME conditions do apply and the site caters to touring caravans, the hook ups would have to be TT.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Caravan park Earthing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
51
Unsolved
--

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Dean074,
Replies
51
Views
11,300

Advert

Back
Top