Is TNS permitted on caravan site? I always thought you could use as TNS as supply cable then TT each pitch, spark I’m working with says you can use TNS all way through if ZS is acceptable
Here we go.
Just because the supply to the installation is TN-S, doesn’t mean PME conditions do not apply.
It’s why BS7671 states “where PME conditions apply”, rather than saying “where the earthing system is TN-C-S”.
Yes ESQCR does prohibit the use of PME for Caravan pitches.
However it does not prohibit the use of PME for static Caravans or for other permanent structures on Caravan sites.
Here we go.
ESQCR are does NOT allow pme conditions to a static caravan! It does allow it for buildings on parks, not the vans themselves
London
Caravan park Earthing
Bradley6969,
Dean074,