View the thread, titled "415v 3 phase sockets and rcd protection." which is posted in UK Electrical Forum on Electricians Forums.
Afternoon all,
Looking for a little guidance, other than doing sub mains in armoured I don’t do much three phase work.
I’m looking to install some final
Circuits for some three phase cooking equipment but I find myself stuck on a few things, as the sockets will be over 16amp they will need to be rcd protected but I can’t seem to find anything to find a Hager board rcbo etc. What’s the best way to protect it?
Also generally if doing a three phase sub main I would take an additional earth as I’m not so keen on solely relying on the armoured earth. Do most people generally rely on the armoured earth or use 5core?
Thanks for your help
I would do 1 of 2 things..
Don’t have the sockets protected by an RCD, subjust to a risk assessment or
Have the appliances hard wired into an isolator, negating the need for RCD protection, subject to installation methods.
You can have an RCD incomer protecting all circuits if necessary..
Have you done any adiabatics?
Sockets with RCDs built in are usually more readily available and a simpler solution than three phase RCBO's, these are often made up from add on modules and quite big taking up 6 ways in a DB.
This mostly comes down to the quality of the glands you use and your ability to fit them correctly. If you fit the correct gland properly then there will be no problem.
If fitting standard surface mount commando sockets with the plastic threaded entry there is rarely room to fit an earth connection to the SWA gland. You may need an adaptable box or besa box to gland the SWA to and make the earth connection or use 5 core cable.
Reply to the thread, titled "415v 3 phase sockets and rcd protection." which is posted in UK Electrical Forum on Electricians Forums.