Afternoon all,
Looking for a little guidance, other than doing sub mains in armoured I don’t do much three phase work.
I’m looking to install some final
Circuits for some three phase cooking equipment but I find myself stuck on a few things, as the sockets will be over 16amp they will need to be rcd protected but I can’t seem to find anything to find a Hager board rcbo etc. What’s the best way to protect it?
Also generally if doing a three phase sub main I would take an additional earth as I’m not so keen on solely relying on the armoured earth. Do most people generally rely on the armoured earth or use 5core?
Thanks for your help
Unless the Manufacturer’s Instructions say otherwise.
Stationary equipment commercial or domestic does not require RCD protection.
However BS7671 now requires all socket-outlets rated 32A and below to be provided with RCD protection unless in non-domestic installations, a documented Risk Assessment concluding RCD protection is provided.
“411.3.3 Additional requirements for socket-outlets and for the supply of mobile equipment for use outdoors
In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:
(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.
An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low voltage systems according to Regulation 411.8.
NOTE 1: See also Regulations 314.1(iv) and 531.3.2 concerning the avoidance of unwanted tripping.
NOTE 2: See Appendix 2, item 11 in respect of risk assessment.
NOTE 3: A lighting distribution unit complying with BS 5733, luminaire track system, installation coupler, LSC or DCL is not regarded as a socket-outlet for the purposes of this regulation.”
Thanks for confirming what I previously said..
Very much appreciated
Or he can come on here and ask for advice on other ways to do the job, saving himself lots of unnecessary work and ultimately saving his client money..
Or you can carry on being obtuse and childish..
you have totally ruined this thread for the op and shown to me that you are very childish and petty
As far as I can see, you’ve offered no constructive advice at all.
All you’ve done is disagree with people who have.
My advice has been to use a socket with built in RCD, rather than installing a hard to obtain RCD at the CU.
Another option would be to use 63A sockets.
As it stands I doubt anyone could legitimately produce a Risk Assessment which concludes RCD protection is not required.
I suggest you read back through the thread from the start!
I have only given constructive advice!
Please prove otherwise..
I have been involved in the installation and repair of commercial catering equipment for 25 years, I am an approved engineer for many brands.
What has been suggested is totally unnecessary..
just because you can’t do something doesn’t mean that it can’t be done, a risk assessment in this instance would be easy enough..
It’s stationary equipment that doesn’t need RCD protection
Im not looking for a way round it, just trying to emphasize that as agreed the stationary equipment doesn’t need RCD protection, it’s totally unnecessary..
RCD protection isn't required for stationary equipment, this does not mean that it is totally unnecessary as you put it. RCD protection could still be installed for stationary equipment over and above the minimum standards set out in bs7671.
However the OP is installing socket outlets, we don't know why they are installing socket outlets, just that they are.
You've made the assumption that the cooking equipment is to be stationary equipment which could reasonably be permanently connected and that the OP is not working to a specification.
Reply to 415v 3 phase sockets and rcd protection. in the UK Electrical Forum area at ElectriciansForums.net
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...