Hi everyone. A recent install I've done on a tt system is giving me a reading of 93.3ohms as a Ze reading. When I then test from my circuits inside I'm getting readings like 106.3 for a socket circuit supplied from 32 amp type b mcb (which should be no higher than 1.10 ohms in bs7671) anyone help me out as to why my meter is giving me these readings ?
It is probably something simple like a bad connection, wobbly rod being kicked by someone, or similar.
Do a few dead tests using a wander lead to confirm the R2 for rod-MET-CU and CU-socket, same for phase to socket L. Poke thing (not while live!) to see if loose or something changes.
Did you take the rod reading at the DB or at the rod, assuming you did it at the rod, have you checked the reading of the connecting cable disconnected from the rod at the DB?
[automerge]1589841330[/automerge]
I installed 3 new rods to get the reading to that
Hope that's in one continuous rod or each outside the zone of influence of the other.
Sorry don't quite understand your response.
From your reply I assume three separate rods connected together, can you tell us the length of the rods, the distance between them, readings from each rod, readings from the rod to the DB and the reading of the cable to the DB disconnected at both ends?
Bed calls.
Sorry Mike dont have the readings on hand. But spike 1 is below the pirelli box. Spike 2 is about 15 meters away and then spike 3 is 10 meters away from spike 2. All spikes are 1m in length
Northern ireland
TT system testing
Timmydoc10,
Mike Johnson,