Hi everyone. A recent install I've done on a tt system is giving me a reading of 93.3ohms as a Ze reading. When I then test from my circuits inside I'm getting readings like 106.3 for a socket circuit supplied from 32 amp type b mcb (which should be no higher than 1.10 ohms in bs7671) anyone help me out as to why my meter is giving me these readings ?
 
It is probably something simple like a bad connection, wobbly rod being kicked by someone, or similar.

Do a few dead tests using a wander lead to confirm the R2 for rod-MET-CU and CU-socket, same for phase to socket L. Poke thing (not while live!) to see if loose or something changes.
 
Did you take the rod reading at the DB or at the rod, assuming you did it at the rod, have you checked the reading of the connecting cable disconnected from the rod at the DB?
[automerge]1589841330[/automerge]
I installed 3 new rods to get the reading to that

Hope that's in one continuous rod or each outside the zone of influence of the other.
 
Did you take the rod reading at the DB or at the rod, assuming you did it at the rod, have you checked the reading of the connecting cable disconnected from the rod at the DB?
[automerge]1589841330[/automerge]


Hope that's in one continuous rod or each outside the zone of influence of the other.
That's with all rods connected
 
Sorry don't quite understand your response.

From your reply I assume three separate rods connected together, can you tell us the length of the rods, the distance between them, readings from each rod, readings from the rod to the DB and the reading of the cable to the DB disconnected at both ends?

Bed calls.
 
Sorry don't quite understand your response.

From your reply I assume three separate rods connected together, can you tell us the length of the rods, the distance between them, readings from each rod, readings from the rod to the DB and the reading of the cable to the DB disconnected at both ends?
Sorry Mike dont have the readings on hand. But spike 1 is below the pirelli box. Spike 2 is about 15 meters away and then spike 3 is 10 meters away from spike 2. All spikes are 1m in length
 

Reply to TT system testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
739
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top