Hi everyone. A recent install I've done on a tt system is giving me a reading of 93.3ohms as a Ze reading. When I then test from my circuits inside I'm getting readings like 106.3 for a socket circuit supplied from 32 amp type b mcb (which should be no higher than 1.10 ohms in bs7671) anyone help me out as to why my meter is giving me these readings ?
 
It is probably something simple like a bad connection, wobbly rod being kicked by someone, or similar.

Do a few dead tests using a wander lead to confirm the R2 for rod-MET-CU and CU-socket, same for phase to socket L. Poke thing (not while live!) to see if loose or something changes.
 
Did you take the rod reading at the DB or at the rod, assuming you did it at the rod, have you checked the reading of the connecting cable disconnected from the rod at the DB?
[automerge]1589841330[/automerge]
I installed 3 new rods to get the reading to that

Hope that's in one continuous rod or each outside the zone of influence of the other.
 
Sorry don't quite understand your response.

From your reply I assume three separate rods connected together, can you tell us the length of the rods, the distance between them, readings from each rod, readings from the rod to the DB and the reading of the cable to the DB disconnected at both ends?

Bed calls.
 
Sorry don't quite understand your response.

From your reply I assume three separate rods connected together, can you tell us the length of the rods, the distance between them, readings from each rod, readings from the rod to the DB and the reading of the cable to the DB disconnected at both ends?
Sorry Mike dont have the readings on hand. But spike 1 is below the pirelli box. Spike 2 is about 15 meters away and then spike 3 is 10 meters away from spike 2. All spikes are 1m in length
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Northern ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
TT system testing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44
Unsolved
--

Advert

Thread statistics

Created
Timmydoc10,
Last reply from
Mike Johnson,
Replies
44
Views
17,391

Advert

TrueNAS JBOD Storage Server

Back
Top